    Line Reactor Ratings

    Line reactor nameplate ratings are typically given in terms of rated inductance and let thru current at a given available fault current at the line side of the reactor at a particular voltage (in my example it's 67uH with a let thru of 9416A with 65kA @ 480VAC applied to the line side of the air-core reactor).

    I'm running a calculation where it's important to know both the x and the r of the reactor. I can calculate the x based on the 67uH inductance. However, in order to calculate r, I believe I would need to know the x/r ratio of the 65kA at the line side of the reactor so I can "back calculate" from the 9416A let thru rating. I don't have a test report available.

    Does anyone know the typical test x/r ratios applied to a line reactor in order to give its nameplate rating (i.e. the x/r ratio of the 65kA on the nameplate)?

  2. #2
    Join Date
    Jan 2016
    Location
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    do they give v drop at rated i ?

    data sheet?
    make mfg?
    wire gauge? length?

  3. #3
    Join Date
    May 2017
    Location
    Arlington Heights, IL, USA
    Posts
    33
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    No they do not, attached is a photo of the nameplate:


    Quote Originally Posted by ish1284 View Post
    Line reactor nameplate ratings are typically given in terms of rated inductance and let thru current at a given available fault current at the line side of the reactor at a particular voltage (in my example it's 67uH with a let thru of 9416A with 65kA @ 480VAC applied to the line side of the air-core reactor).

    I'm running a calculation where it's important to know both the x and the r of the reactor. I can calculate the x based on the 67uH inductance. However, in order to calculate r, I believe I would need to know the x/r ratio of the 65kA at the line side of the reactor so I can "back calculate" from the 9416A let thru rating. I don't have a test report available.

    Does anyone know the typical test x/r ratios applied to a line reactor in order to give its nameplate rating (i.e. the x/r ratio of the 65kA on the nameplate)?
    Attached Images Attached Images  
    Last edited by ish1284; 07-09-18 at 12:21 PM. Reason: Not legible photo

  4. #4
    Join Date
    Jan 2016
    Location
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    can't see the kvar?

  5. #5
    Join Date
    Jan 2016
    Location
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    X = 2 Pi 60 67 uH = 25.2584 mOhm

    i fault reactive = 480/2X = 9501.7876 A, rated 9416
    the difference is r
    Z = 480/9416/2 = 25.4885 mOhm
    R = sqrt(Z^2 - X^2) = 3.4174 mOhm

    X/R = 7.39
    pf = 0.134

    I think, let me look at it some more

  6. #6
    Join Date
    May 2017
    Location
    Arlington Heights, IL, USA
    Posts
    33
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ish1284 View Post
    No they do not, attached is a photo of the nameplate:
    My bad, kVAR is 491

  7. #7
    Join Date
    May 2017
    Location
    Arlington Heights, IL, USA
    Posts
    33
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Your calculated x/r seems pretty low and not sure what the factor of 2 you have in there is for. Looks like you're missing a sqrt(3) factor.

    I have a test report for a smaller model made by the same mfg and the x/r came out to be ~65. I'd expect something closer to that.

    The x/r ratio of the 65kA it is rated for also plays a role in the let thru current on the other side. The 480/z that you calculated below also includes the source impedance. The impedance of the source needs to be split out from the impedance of the reactor. X/R of a line reactor should be pretty high because it's primarily reactance.


    Quote Originally Posted by Ingenieur View Post
    X = 2 Pi 60 67 uH = 25.2584 mOhm

    i fault reactive = 480/2X = 9501.7876 A, rated 9416
    the difference is r
    Z = 480/9416/2 = 25.4885 mOhm
    R = sqrt(Z^2 - X^2) = 3.4174 mOhm

    X/R = 7.39
    pf = 0.134

    I think, let me look at it some more

  8. #8
    Join Date
    Jan 2016
    Location
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ish1284 View Post
    Your calculated x/r seems pretty low and not sure what the factor of 2 you have in there is for. Looks like you're missing a sqrt(3) factor.

    I have a test report for a smaller model made by the same mfg and the x/r came out to be ~65. I'd expect something closer to that.

    The x/r ratio of the 65kA it is rated for also plays a role in the let thru current on the other side. The 480/z that you calculated below also includes the source impedance. The impedance of the source needs to be split out from the impedance of the reactor. X/R of a line reactor should be pretty high because it's primarily reactance.
    I looked at it as a 480 ph-ph
    this would involve 2 reactors (the 480 with be 1ph, but I guess you could use sqrt3)
    this equates to a ph ang of 83 deg
    what is the current rating?

    S fault ~ 54.0400 Mva
    1ph source Z ~ 480/(1.732 x 65000) = 4.2635 mOhm, 7.3846 3ph
    1ph reactor Xl = 25.2584, 3ph 43.7488

    total Z = 480/9415 = 50.9825 3ph, 1ph 29.4847
    reactor Z = total - source = 43.5979 3ph
    but reactor X > Z so R can't be calculated

    it appears that rounding the ratings prevents calc R
    but it looks like x/r >100 is a safe assumption

  9. #9
    Join Date
    May 2017
    Location
    Arlington Heights, IL, USA
    Posts
    33
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Ingenieur View Post
    I looked at it as a 480 ph-ph
    this would involve 2 reactors (the 480 with be 1ph, but I guess you could use sqrt3)
    this equates to a ph ang of 83 deg
    what is the current rating?

    S fault ~ 54.0400 Mva
    1ph source Z ~ 480/(1.732 x 65000) = 4.2635 mOhm, 7.3846 3ph
    1ph reactor Xl = 25.2584, 3ph 43.7488

    total Z = 480/9415 = 50.9825 3ph, 1ph 29.4847
    reactor Z = total - source = 43.5979 3ph
    but reactor X > Z so R can't be calculated

    it appears that rounding the ratings prevents calc R
    but it looks like x/r >100 is a safe assumption
    I think we've gotten a little off topic from the original question. I'm not looking to make an assumption. I'm looking to see if there's a standard testing procedure that defines the test x/r ratio required rate a series reactor. Similar to the test x/r ratios required to rate circuit breakers (i.e. UL489).

  10. #10
    Join Date
    Nov 2007
    Posts
    940
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ish1284 View Post
    I think we've gotten a little off topic from the original question. I'm not looking to make an assumption. I'm looking to see if there's a standard testing procedure that defines the test x/r ratio required rate a series reactor. Similar to the test x/r ratios required to rate circuit breakers (i.e. UL489).
    Why go through the trouble of testing for x/r when you can just test for x and then r?
    For the test on x, you impress a suitable voltage and measure the current and apply the necessary computations and get x. For r, you need a voltage source with near zero frequency and use a wheatstone bridge to get the resistance.