Results 1 to 10 of 10
Thread: Does a 1200A switchboard have to be freestanding or can it be wall mounted?
  1. #1
    Join Date
    Jul 2015
    Indianapolis
    Posts
    17
    I am in Chicago, spoke to a city's electrical inspector and he said it used to be required in the past that a switchboard over 2 sections must be freestanding.
    He referred to section 384 of the Chicago Electrical Code (CEC), but I couldn't find it anywhere.
    Now that Chicago has adopted the NEC with amendments, I still can't find a requirement for free standing switchboards.
    My question are:
    1. If this was indeed an old Chicago requirements, which year and which code section was it, I can't find any?
    2. Is a 1200A switchboard required to be free standing based on NEC 2017?
    Thank You
  2. #2
    Join Date
    Aug 2004
    Northern illinois
    Posts
    16,930
    https://chicagocode.org/18/18-27/
    ยง 18-27-384.8
    Clearances
    a.
    From Ceiling. A space of not less than 3 ft (914 mm) shall be provided between the top of the switchboard and any combustible ceiling.
    b.Around Switchboards. Clearances around switchboards shall comply with the provisions of Section 18-27-110.26 and Section 18-27-384.4.
    c. Free Standing. Switchboards over two sections wide or over 30 in. (762 mm) deep shall be free standing and shall have a minimum of 24 in. (610 mm) end clearances to walls or adjacent switchboards.
    Bob
  3. #3
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,018
    Anyone want to take a shot at what this actually means?
    Rob
    All responses based on the 2014 NEC unless otherwise noted
  4. #4
    Join Date
    Jul 2015
    Indianapolis
    Posts
    17
    I checked the 2011 NEC, I dont have access to the 2014 or 2017 NEC.
    It's moved to section 408.18. (A) and (B) are still there, (C) which is the freestanding note, is deleted.
    I suppose wall-mounted switchboards are OK, unless the experts here disagree.
  5. #5
    Join Date
    Aug 2004
    Northern illinois
    Posts
    16,930
    Quote Originally Posted by infinity View Post
    Seems faily straightforward to me.
    Bob
  6. #6
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,018
    So the switchboard is 36" wide it cannot be mounted to a the wall if it's on the floor?
    Rob
  7. #7
    Join Date
    Aug 2004
    Northern illinois
    Posts
    16,930
    it does not say that at all.
    It says if it is over 30" deep or more than 2 sections wide it must be free standing and have 2 feet clear space on each end.
    I think a good definition of free standing is that it is not up against anything else such as a wall. Interestingly, it does not say how much clearance is required behind the free standing switchboard, so likely they enforce the clearances mentioned earlier in the requirement.
    Bob
  8. #8
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,018
    Quote Originally Posted by petersonra View Post
    That was kind of my point it says nothing about being against the wall behind it and the OP asked about wall mounted. I agree that the words free standing mean that it's sitting on the floor and the wall behind it can be there but it doesn't need to be.
    Rob
  9. #9
    Join Date
    Feb 2003
    Illinois
    Posts
    23,752
    The language does not match what I was told when working on a job under the Chicago code. What I was told is that they wanted clearance on the back side of the gear, to allow access.
    Taking a quick look at their 2018 code, which is the 2017 NEC with 150 pages of amendments, I don't see any amendments to Articles 110 or 408.
    I only took a quick look, so I could have missed it. You can view the ordinance showing the amendments from a link on this page. This version of their code became effective in March of this year. The Chicago code is now published by the NFPA and can be purchased from them.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)
  10. #10
    Join Date
    Jul 2006
    Posts
    8,113
    Makes me wonder what sort of hack job someone did to make them require this to be stated...
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
Posting Permissions
  • You may not post replies
  • You may not edit your posts