    Have a lot of 1/c #4/0 15kv cable CU that they want us to VE to AL. How would I approach this to account for the correct AL size cable? Thanks.
  2. #2
    Join Date
    Dec 2008
    Posts
    557
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    At first you have to state a few details:
    -current [normal, short-circuit]
    -cable route [for instance: underground, conduit, duct, RHO, ambient temperature]
    -how many cables per conduit or duct or tray or else.
  3. #3
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    wag
    you want the same cable type, insul, etc
    in Al with an ampacity equal to Cu 4/0 unless the Cu is oversized, then base on load i
    it may impact conduit size
    you could also look at C, L and R for equivilence