    220.87 Meter Readings

    This is an excerpt of the meter billing on a project I am quoting.
    the 1.58 in the Demand Rdg column is the highest over a two year period.
    How do I use this for 220.87 Determining Existing Loads?



    Tony Hill

  2. #2
    Join Date
    Jun 2004
    Location
    North Central Texas
    Posts
    929
    you probably can't read that, but I don't know how to enhance it
    Tony Hill

  3. #3
    Join Date
    Jun 2004
    Location
    North Central Texas
    Posts
    929
    The columns read:
    Reading......Usage/day.....Billing Mult...............Demand Rdg .............Demand Rdg Dt/Tm...........KWH Usage/Day
    20125..........4...................60............. ..............1.58..........................03/01/2018 00:00:00 4 X60
    Tony Hill

  4. #4
    Join Date
    Jun 2004
    Location
    North Central Texas
    Posts
    929
    Service is 208Y/120V.
    Original load calculation on panel schedule was 186.539KW = 518 Amps.
    heat load was 91KW
    Tony Hill

  5. #5
    Join Date
    Jun 2004
    Location
    North Central Texas
    Posts
    929
    So, what I'm thinking is you multiply the 1.58 times that multiplier of 60 which would give me 94.8KVA which would be about what I would expect in the dead of winter with 90kw of heat in the building.
    Multiply that by 1.25 per 220.87 gives me 118.5KVA.
    600 AMP 208 service = 216KVA
    216 - 118.5 = 97.5KVA or 260 amps available.

    Am I thinking right on this?
    Tony Hill