    We have (3) outdoor gas turbine generators (480v/3ph, 1MW each)
    power a 480v/3ph parallel switchgear also sits outside.
    The switchgear is then feeds a step up 480v:5KV transformer,
    the output of xfmr connect to an existing underground 5KV feeder
    at one end, the other end of this 5KV feeder is powered from utility
    as backup source via a MV switch (note: this 5KV feeder feeds
    several buildings in the area)
    Question: Does nec require to ground the parallel switchgear
    above? i.e bond neutral to equipment ground bus
    and then connnect to the ground rod, maybe?
    All turbine generarors were grounded via a ground wire connect all
    generarors and binddto a triad ground rods.
  2. #2
    Join Date
    Feb 2003
    New York, 40.7514,-73.9925
    Posts
    4,658
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    There is a lot of detail missing and I think without a oneline showing where all the N-G bonds and grounds, grounding electrode conductors and grounding electrodes are, an incomplete answer will be given.
    Can you describe or draw this?
    Ron
  3. #3
    Join Date
    Feb 2003
    Bremerton, Washington
    Posts
    8,044
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    And please use the NEC terms instead of the generic "ground", on a drawing or description. Are these generators separately derived?
    Moderator-Washington State
    Ancora Imparo
  4. #4
    Join Date
    Jun 2007
    Posts
    760
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ron View Post
    See attached.
    Attached Images Attached Images
  5. #5
    Join Date
    Feb 2003
    Posts
    4,658
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Since the Gens have N-G bonds, then a N-G bond is not installed at the parallel gear.
    The middle gen should be routed to the grounding electrodes directly.
    I am surprised that it is 4W+G from the gens to the parallel gear. Typically I would think it is 3W+G, not 4W+G since there is a N-G bond at the gens. Who needs to waste the extra conductors.
    Ron
  6. #6
    Join Date
    Jun 2007
    Posts
    760
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Can we not ground the middle generator
    as you wrote?