    Receptacle placement requirements in schools

    What are or where can I find receptacle placement requirements for schools?

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,306
    Is this what you are looking for? There are a few exceptions

    406.12 Tamper-Resistant Receptacles. All 15- and 20-ampere,
    125- and 250-volt nonlocking-type receptacles in the areas
    specified in 406.12(1) through (7) shall be listed tamperresistant
    receptacles.
    (1) Dwelling units in all areas specified in 210.52 and 550.13
    (2) Guest rooms and guest suites of hotels and motels
    (3) Child care facilities
    (4) Preschools and elementary education facilities
    (5) Business offices, corridors, waiting rooms and the like in
    clinics, medical and dental offices and outpatient facilities
    (6) Subset of assembly occupancies described in 518.2 to
    include places of waiting transportation, gymnasiums,
    skating rinks, and auditoriums
    (7) Dormitories
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #3
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,165
    Along with Dennis's post there is Part III of article 210.

    Roger
    Moderator

  4. #4
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,620
    There are almost no requirements for receptacles for non-dwelling occupancies. It is left to the designer for the most part.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)

  5. #5
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    7,868
    As Don mentioned, the NEC for non dwelling locations only has a few receptacle req: Electrical service area, HVAC, conference rooms. Now those recepts, where installed may need to be GFCI.