    200amp service

    Good evening,

    I’m in the state of Massachusetts (don’t know if State matters) but I’m installing a 200 amp underground service. I’m installing the panel more than 10 feet away so I will need a disconnect.
    My question is does the panel need to be a main breaker panel or main lug panel? Or is either one acceptable? Thanks in advance.

  2. #2
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    23,004
    Quote Originally Posted by pmoney44 View Post
    My question is does the panel need to be a main breaker panel or main lug panel? Or is either one acceptable? Thanks in advance.
    Either is acceptable. You're welcome.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA