    Equipment space

    I have to upgrade this panel and service I'm 100%certin that steam line is in the dedicated space and I need to move the panel anyone disagree

    Sent from my SM-G950U using Tapatalk

  2. #2
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,802
    Moving the panel is a good start. Looks like you are going to be there all month.
    If you don't think too good, don't think too much.

  3. #3
    Join Date
    Oct 2015
    Location
    US
    Posts
    689
    If I installed the new panel under the steam line would it still be considered inside the space

    Sent from my SM-G950U using Tapatalk

  4. #4
    Join Date
    Dec 2010
    Posts
    1,427
    Quote Originally Posted by nickelec View Post
    I have to upgrade this panel and service I'm 100%certin that steam line is in the dedicated space and I need to move the panel anyone disagree

    Sent from my SM-G950U using Tapatalk
    It doesn't seem to be in the dedicated space, but does appear to be in the working space.
    The more they overthink the plumbing, the easier it is to stop up the drain

  5. #5
    Join Date
    Oct 2015
    Location
    US
    Posts
    689
    So if that steamline were 6 foot 7inches off the floor and the panel is mounted underneath it then I would be in the clear correct

    Sent from my SM-G950U using Tapatalk

  6. #6
    Join Date
    Jan 2013
    Location
    Albuquerque, New Mexico ,Untied States of America
    Posts
    279
    I believe he is referring to the front working space, the steam line is not your only problem...the cabinet that the panel is in is considered in the working space IIRC.

    Quote Originally Posted by nickelec View Post
    So if that steamline were 6 foot 7inches off the floor and the panel is mounted underneath it then I would be in the clear correct

    Sent from my SM-G950U using Tapatalk
    PJHolguin 8-)

  7. #7
    Join Date
    Oct 2015
    Location
    US
    Posts
    689
    Cabinetis coming down when u replace the panel im worried about the steam line

    Sent from my SM-G950U using Tapatalk

  8. #8
    Join Date
    Dec 2011
    Location
    Wisconsin
    Posts
    481
    Quote Originally Posted by nickelec View Post
    So if that steamline were 6 foot 7inches off the floor and the panel is mounted underneath it then I would be in the clear correct

    Sent from my SM-G950U using Tapatalk
    110.26(E)-Dedicate equipment space is the space above the panel, the width and depth of the panel and up to 6 feet above the panel or to the structural ceiling (whichever is lower), and cannot anything other than that which is dedicated to the electrical installation (cables, raceways, etc.).

    110.26(A)(1) through (3)- Clear working space is the space in front of the panel, 30 inches wide by 36 inches deep and 6.5 feet high, and this space cannot contain anything else.

    If the steam pipe is in either of the above spaces, it would be a violation.

  9. #9
    Join Date
    Feb 2003
    Location
    Seattle, WA
    Posts
    19,184
    My review of the photo tells me that the steam line is not directly over the panel. So you would not have a problem with dedicated space. It then would come down to whether the steam line is at least 6.5 feet above the floor.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.

  10. #10
    Join Date
    May 2013
    Location
    Massachusetts
    Posts
    2,412
    Quote Originally Posted by packersparky View Post
    110.26(E)-Dedicate equipment space is the space above the panel, the width and depth of the panel and up to 6 feet above the panel or to the structural ceiling (whichever is lower), and cannot anything other than that which is dedicated to the electrical installation (cables, raceways, etc.).

    110.26(A)(1) through (3)- Clear working space is the space in front of the panel, 30 inches wide by 36 inches deep and 6.5 feet high, and this space cannot contain anything else.

    If the steam pipe is in either of the above spaces, it would be a violation.
    How does dedicated space apply to panelboards recessed in wood framing? Are cross-members of the wood framing and thermal insulation allowed within it?