    Possible voltage drop

    I'm staying at a RV park, there has pretty much been 0 upkeep in the past 32 years, I noticed throughout the day the voltage fluctuates quite a bit between 93V and 117v, I've checked power at the post a few times and its usually a couple volts higher than inside the camper, I'm looking for some type of solution to keep the voltage up, any ideas?
    Click image for larger version. 

Name:	IMG-20180711-WA0000.jpg 
Views:	172 
Size:	140.6 KB 
ID:	20754

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,875
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I would suspect a bad neutral connection somewhere.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Dec 2015
    Location
    United States
    Posts
    90
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Maybe I'll do some more poking around, I wouldn't doubt multiple lots being on the same circuit also, as most of the wiring appears to be overhead strung through the trees

  4. #4
    Join Date
    May 2018
    Location
    Boyertown, PA, USA
    Posts
    508
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You could do what I did: I sold the RV park a complete upgrade. It had six paired "pedestals" (18" tall 6x6 posts) each with a pair of duplex Edison receptacles on an ungrounded bootlegged multi-wire 60a circuit that used the bare conductor as a neutral. The feeder was 375 feet of 6awg buried about 4" deep. Guests frequently parked, saw the power situation, demanded a refund and left.

    I installed two 200amp services feeding 12 Midwest pedestals with 50/30/20 receptacles via 4/0 in conduit 30" down.

    Honestly, there's nothing you as a guest can do to stabilize the voltage to your site.

  5. #5
    Join Date
    Dec 2015
    Location
    United States
    Posts
    90
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I highly doubt these people put any money into this place, and they only accept cash, sevral lots are vacant because of power or water/sewer issues, the post appears to have a #2 or #3 aluminum feeding my whole row, most likely on a 200/250amp fuse, , which has 6 campers in use, both lugs were loose but after tightening did not appear to improve the issue,
    Click image for larger version. 

Name:	rps20180712_201420.jpg 
Views:	89 
Size:	116.1 KB 
ID:	20755
    Click image for larger version. 

Name:	rps20180712_201537.jpg 
Views:	92 
Size:	101.9 KB 
ID:	20756
    Click image for larger version. 

Name:	rps20180712_201735.jpg 
Views:	88 
Size:	120.6 KB 
ID:	20757

  6. #6
    Join Date
    Jul 2013
    Location
    Arcata, CA
    Posts
    437
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by karn View Post
    I'm looking for some type of solution to keep the voltage up, any ideas?
    Click image for larger version. 

Name:	IMG-20180711-WA0000.jpg 
Views:	172 
Size:	140.6 KB 
ID:	20754
    Move to a different park.

  7. #7
    Join Date
    Dec 2015
    Location
    United States
    Posts
    90
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Barbqranch View Post
    Move to a different park.
    I would if I could (: I may try to torque up those exposed lugs In the bottom of the main and see if that helps, but I almost wonder if the issue may be the transformer dropping under a heavy load or something else

  8. #8
    Join Date
    Jul 2013
    Location
    Renton, WA
    Posts
    947
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    hook up your scope to the line, waveforms will tell you if transformer drop is involved.

  9. #9
    Join Date
    Dec 2015
    Location
    United States
    Posts
    90
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by junkhound View Post
    hook up your scope to the line, waveforms will tell you if transformer drop is involved.
    Unfortunately I don't have a scope, and probably wouldn't be able to read it well enough if I did

  10. #10
    Join Date
    May 2018
    Location
    Boyertown, PA, USA
    Posts
    508
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by karn View Post
    I would if I could (: I may try to torque up those exposed lugs In the bottom of the main and see if that helps, but I almost wonder if the issue may be the transformer dropping under a heavy load or something else
    Six 30 amp campers pulling through 2AWG aluminum feeder that likely needs all the connections cleaned and retreated with anti-oxidation compound...it's actually somewhat surprising you see 93v.