Results 1 to 4 of 4

Thread: can't find it

  1. #1
    Join Date
    Feb 2008
    Location
    San Antonio, Texas
    Posts
    658

    can't find it

    What articles cover the size of grounded & grounding conductors required for:
    #6 THWN on a 60 amp breaker? Been a hectic day, & can't find it now.

  2. #2
    Join Date
    Dec 2011
    Location
    Wisconsin
    Posts
    350
    Equipment grounding conductors- 250.122
    Grounding electrode conductors-250.66
    Grounded conductors, bonding conductors and jumpers-250.102

  3. #3
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,314
    Remember the T250.104 is for the smallest sized grounded conductor allowed for a service. The smallest grounded conductor for a feeder would be based on 250.122.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  4. #4
    Join Date
    Dec 2011
    Location
    Wisconsin
    Posts
    350
    Quote Originally Posted by Dennis Alwon View Post
    Remember the T250.104 is for the smallest sized grounded conductor allowed for a service. The smallest grounded conductor for a feeder would be based on 250.122.
    Dennis, there is no table for 250.104. 250.104 references you back to Table 250.102(C)(1) for sizing of bonding conductors.