    Sub feed

    I think all feeders and sub feeds for panels need bonding bushings, but what if i use a chase nipple to connect the two panels or panel to gutter, I suppose you could still get the bonding bushings on one side but if they are connected using a rigid coupling as a raceway then what? I'm also not sure rigid couplings are listed as raceways or if it would be a legit install but theoretically a close nipple could be cut to fit inside the coupling

  2. #2
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,928
    Quote Originally Posted by karn View Post
    I think all feeders and sub feeds for panels need bonding bushings, but what if i use a chase nipple to connect the two panels or panel to gutter, I suppose you could still get the bonding bushings on one side but if they are connected using a rigid coupling as a raceway then what? I'm also not sure rigid couplings are listed as raceways or if it would be a legit install but theoretically a close nipple could be cut to fit inside the coupling
    why do you think this?
    Bob

  3. #3
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    7,960
    Perhaps a better question is why does the NEC require special bonding on service conductors?
    Hint: They are called "unfused service entrance conductors" by the trade
    Knowing the why leads you to the how.
    Moderator-Washington State
    Ancora Imparo

  4. #4
    Join Date
    Dec 2015
    Location
    United States
    Posts
    88
    It's just what I've always done, I never actually read in detail the specifics of the code but it makes sense since you put it that way,, and I'm not calling the shots on this job, I'm just here helping out and noticed two panels side by side with the chase nipples and couplings for the parallel feed to the sub panel and wondered about the specifics of a code legal way for that install to work

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,013
    Quote Originally Posted by karn View Post
    It's just what I've always done, I never actually read in detail the specifics of the code but it makes sense since you put it that way,, and I'm not calling the shots on this job, I'm just here helping out and noticed two panels side by side with the chase nipples and couplings for the parallel feed to the sub panel and wondered about the specifics of a code legal way for that install to work
    Chase nipples and rigid coupling are not code compliant. You should be using a rigid nipple or other raceway. This is NG:

    Name:  IMG_20150218_100418.jpg
Views: 120
Size:  126.9 KB
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted