Results 1 to 5 of 5
Thread: Communications Cable Installation Methods - Basement
  1. #1
    Join Date
    May 2018
    Boston
    Posts
    39
    Running communications cables (tele/data) in exposed basements; I went thru article 800 and it's not too clear to me.
    Are communication cables run in exposed basements (apt. buildings) required to be in raceways or not?
    Thanks
  2. #2
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    23,718
    I have used NM stackers for LV wiring in basements. I believe raceway use would be determined by damage exposure.
    Click image for larger version.
ID:	20770 Click image for larger version.
    Click thumbnails for close-ups.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  3. #3
    Join Date
    May 2018
    Boston
    Posts
    39
    Thank you Larry.
    Is that for a single dwelling unit or for a larger type apt building?
  4. #4
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    23,718
    Those pics are from a single-family house, over 7K sq. ft. (The basement alone is over 3K sq. ft.)
    Larry B. Fine
    Master Electrician
    Richmond, VA
  5. #5
    Join Date
    Jun 2003
    Hawthorne, New York NEC: 2014
    Posts
    3,977
    The NEC doesn't care how you run your cables as long as you don't use existing wiring, conduits plumbing, sprinkler pipes or ceiling support wires to support them. Only other concern is the fire rating of the cable, use plenum in air handling spaces above ceilings and riser cable for vertical runs extending up through several floors. I generally only stock at least riser rated cable.
    Depending on the ceiling material use what ever is convenient, you certainly don't need conduit. I normally use drive rings or Caddy "J" hooks.
    -Hal