Thread: PV exceeds max allowable backfeed. True?

  1. #31
    Join Date
    Nov 2015
    Location
    CA, USA
    Posts
    681
    Quote Originally Posted by Coppersmith View Post
    Well, the real reason is because the solar contractor made a mistake and told the HO that it could be done in a subpanel. He then recommended me to the HO to install the subpanel. The HO hired me to do the install and it's complete. Now the solar contractor's engineer (who got involved late in the project) is saying "No no no, you need a line side tap." I'm trying to save him some embarrassment by finding a way to use the load side connection.
    Never try to ask forgiveness from an engineer. If an engineer is going to be part of the project bring them in early and ask permission. Makes life much simpler.

  2. #32
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    1,847
    Quote Originally Posted by pv_n00b View Post
    Never try to ask forgiveness from an engineer. If an engineer is going to be part of the project bring them in early and ask permission. Makes life much simpler.
    You're preaching to the choir. I just do what they pay me to do and offer advice when I see trouble brewing. I could not foretell this situation due to my ignorance of the PV section of NEC. I now am a lot more knowledgeable. (I don't admit ignorance lightly. )

  3. #33
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    10,174
    Quote Originally Posted by pv_n00b View Post
    Never try to ask forgiveness from an engineer. If an engineer is going to be part of the project bring them in early and ask permission. Makes life much simpler.
    Well, if that "forgiveness" means letting a code violation slide, the engineer would have no business granting it. I certainly wouldn't.

  4. #34
    Join Date
    Dec 2017
    Location
    CA
    Posts
    11
    Quote Originally Posted by jaggedben View Post
    ??? That doesn't help.
    Sorry I misread something. But why don’t you get rid of two modules?

  5. #35
    Join Date
    May 2011
    Posts
    4,693
    Quote Originally Posted by baserunner4 View Post
    Sorry I misread something. But why don’t you get rid of two modules?
    That's an option, too, technically. But no one wants to present that option to the customer unless one has a solid clause in the contract that allows for charging more for other options. I don't think I've ever proposed it when a supply side connection was feasible.

  6. #36
    Join Date
    Dec 2017
    Location
    CA
    Posts
    11
    Quote Originally Posted by jaggedben View Post
    That's an option, too, technically. But no one wants to present that option to the customer unless one has a solid clause in the contract that allows for charging more for other options. I don't think I've ever proposed it when a supply side connection was feasible.
    Have you looked at 705.12(D)(2)(3)(c)?

  7. #37
    Join Date
    May 2011
    Posts
    4,693
    Quote Originally Posted by baserunner4 View Post
    Have you looked at 705.12(D)(2)(3)(c)?
    Yes, I mentioned it in post #2.

  8. #38
    Join Date
    Nov 2015
    Location
    CA, USA
    Posts
    681
    Quote Originally Posted by ggunn View Post
    Well, if that "forgiveness" means letting a code violation slide, the engineer would have no business granting it. I certainly wouldn't.
    Sometimes what looks like a code violation can be turned into an Alternative Means and Materials exception by a good engineer and AHJ working together. I've saved a couple of projects doing this when the designer or contractor screwed up an installation and it would be costly to go back and make it code compliant. But sometimes there is no way to save it and make it safe. In that case, someone just has to eat it and make it right. Plus the tears of a designer or contractor who gets in this position because they don't quite know what they are doing taste like rainbows.

  9. #39
    Join Date
    May 2011
    Posts
    4,693
    Quote Originally Posted by pv_n00b View Post
    ...Plus the tears of a designer or contractor who gets in this position because they don't quite know what they are doing taste like rainbows.