Thread: open paint spray area - explosion proof outlet requirement?

  1. #1
    Join Date
    Jun 2007
    Posts
    752

    open paint spray area - explosion proof outlet requirement?

    If the bldg. has an open paint spray area and there are both power and data outlets
    located within the area, should these outlets need to be explosion proof type?
    this seems odd, especially the data outlets. I am not sure they make one?
    Are there any exceptions from code? Thank you.

  2. #2
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,751
    You need to define the classified area limits to know what type of equipment needs to be installed. Take a look at Article 516. The area can be extensive.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)

  3. #3
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,117
    Quote Originally Posted by anbm View Post
    If the bldg. has an open paint spray area and there are both power and data outlets
    located within the area, should these outlets need to be explosion proof type?
    this seems odd, especially the data outlets. I am not sure they make one?
    Are there any exceptions from code? Thank you.
    Before you go slapping XP devices around the place, someone needs to formally decide what the area classification is so the proper boundaries can be established.

  4. #4
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,930
    Quote Originally Posted by anbm View Post
    If the bldg. has an open paint spray area and there are both power and data outlets
    located within the area, should these outlets need to be explosion proof type?
    this seems odd, especially the data outlets. I am not sure they make one?
    Are there any exceptions from code? Thank you.
    I never heard fo an XP data outlet but they do make IS barriers that work on such circuits.

    having said that, what would you be able to plug into a comm link in a classified area anyway? there are such things available but not real cheap.
    Bob

  5. #5
    Join Date
    Jun 2007
    Posts
    752
    Quote Originally Posted by don_resqcapt19 View Post
    You need to define the classified area limits to know what type of equipment needs to be installed. Take a look at Article 516. The area can be extensive.
    The whole space is considering open spray area with cranes moving back and forth above, so I assume class 1, div. 1 area?

  6. #6
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,117
    Quote Originally Posted by anbm View Post
    The whole space is considering open spray area with cranes moving back and forth above, so I assume class 1, div. 1 area?
    What are you spraying? Latex paints? Oil-based? What is the volume of VOC's generated per unit time? What is the area/volume of the spray operations compared to the area/volume of the whole space? What is the interior volume? You can just say Class I Div 1, but then you probably can't do a lot of what you're doing right now.

  7. #7
    Join Date
    Jun 2007
    Posts
    752
    Quote Originally Posted by gadfly56 View Post
    What are you spraying? Latex paints? Oil-based? What is the volume of VOC's generated per unit time? What is the area/volume of the spray operations compared to the area/volume of the whole space? What is the interior volume? You can just say Class I Div 1, but then you probably can't do a lot of what you're doing right now.
    What is your point? Will any of the creterias
    you listed above make us get away from
    installing explosionproof outlets?

  8. #8
    Join Date
    Jul 2017
    Location
    Alberta, Canada
    Posts
    41
    Quote Originally Posted by anbm View Post
    What is your point? Will any of the creterias you listed above make us get away from installing explosionproof outlets?
    Yes, certainly. Not all paints will form an explosive atmosphere, and the other criteria will determine extent of area. Maybe your outlets will be in a Div 2 area, or outside the hazardous area completely.