    Old houses , 406.4(D)(2)(c) and 250.114

    Situation: Old house with 2-wire NM cable concealed in the walls, not feasible to replace the cable or add a ground wire.

    406.4(D)(2)(c) seems to permit the use of 3-conductor grounding-type receptacles if they're ground-fault protected and labeled.
    But 250.114 seems to require certain appliances to be grounded, apparently without exceptions.

    Two questions come to mind:
    Does anybody know of a source of cover plates permanently engraved with the required messages "GFCI Protected" and "No Equipment Ground"? Sharpies look unprofessional and Post-It notes lack permanence.

    Does 250.114 supersede 406.4(D)(2)(c), and if so, in the case of a non-double-insulated window air conditioner (among other appliances) with a 3-wire cord and a 3-conductor plug,
    how is the average homeowner/tenant supposed to know that the normally non-current-carrying metals parts shall be connected to an equipment-grounding conductor, and they're not supposed to plug it into a 3-conductor receptacle so labeled?

  2. #2
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,531
    Quote Originally Posted by drcampbell View Post
    Does anybody know of a source of cover plates permanently engraved with the required messages "GFCI Protected" and "No Equipment Ground"? Sharpies look unprofessional and Post-It notes lack permanence.
    No but GFCI receps come with those stickers. Or Wal mart has a label maker for $25. Yeah its a stupid requirement. Non electricians have no idea what that means. I remember seeing some of those label outlets as a teenager before I got into electrical and had no idea what it meant :
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  3. #3
    Join Date
    Jul 2005
    Location
    LA basin, CA
    Posts
    1,809
    Quote Originally Posted by drcampbell View Post
    ..Does 250.114 supersede 406.4(D)(2)(c)..
    Notice 250.114 is limited to “Equipment.” Not branch circuits. The authority of 250.114 ends at the appliance cord and plug, in agreement with NRTL listing requirements for appliance construction requirements.

    406.4(D) prevails, since a 3-prong corded appliances with low level fault is extnguished near 6ma with class-A GFCI protection, and saves lives long before a grounding wire can overload the 20A fuse.
    Roger Ramjet NoFixNoPay

  4. #4
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    1,479
    I've passed so many of these with DF's , but they are not the end all cure for no EGC

    Wasn't there a recent change that allowed us to utilize any available ECG from proximal circutry?

    I can't seem to find it....

    ~RJ~

  5. #5
    Join Date
    Jul 2007
    Location
    Iowegia
    Posts
    17,948
    Quote Originally Posted by drcampbell View Post
    ..............Does 250.114 supersede 406.4(D)(2)(c), and if so, in the case of a non-double-insulated window air conditioner (among other appliances) with a 3-wire cord and a 3-conductor plug,............
    No.

    406 modifies the requirements of 250.114.

  6. #6
    Join Date
    Mar 2016
    Location
    The Motor City, Michigan USA
    Posts
    765
    Quote Originally Posted by romex jockey View Post
    I've passed so many of these with DF's ...
    What's a DF? (TMA Syndrome)

  7. #7
    Join Date
    Dec 2010
    Location
    Tennessee NEC:2008
    Posts
    4,737
    Pretty sure he was talking about Dual Function AFCI/GFCI breakers
    If you aim at nothing, you will hit it every time!

  8. #8
    Join Date
    Sep 2008
    Location
    UK
    Posts
    11,777
    Quote Originally Posted by drcampbell View Post
    Situation: Old house with 2-wire NM cable concealed in the walls, not feasible to replace the cable or add a ground wire.

    406.4(D)(2)(c) seems to permit the use of 3-conductor grounding-type receptacles if they're ground-fault protected and labeled.
    But 250.114 seems to require certain appliances to be grounded, apparently without exceptions.

    Two questions come to mind:
    Does anybody know of a source of cover plates permanently engraved with the required messages "GFCI Protected" and "No Equipment Ground"? Sharpies look unprofessional and Post-It notes lack permanence.

    Does 250.114 supersede 406.4(D)(2)(c), and if so, in the case of a non-double-insulated window air conditioner (among other appliances) with a 3-wire cord and a 3-conductor plug,
    how is the average homeowner/tenant supposed to know that the normally non-current-carrying metals parts shall be connected to an equipment-grounding conductor, and they're not supposed to plug it into a 3-conductor receptacle so labeled?
    Just out of interest, how old is old?
    Si hoc legere scis nimium eruditionis habes.

  9. #9
    Join Date
    Mar 2016
    Location
    The Motor City, Michigan USA
    Posts
    765
    This question has come up more than once, but the house we're currently working on was probably built in the 1920s (some pre-NEMA receptacles, bare-bulb ceiling light fixtures, tar-impregnated cotton sleeves) and upgraded in the 1940s or 1950s. (knotty-pine finished basement, 12-circuit fuseboxes)

  10. #10
    Join Date
    Nov 2007
    Location
    Livonia, Michigan
    Posts
    276
    Quote Originally Posted by drcampbell View Post
    This question has come up more than once, but the house we're currently working on was probably built in the 1920s (some pre-NEMA receptacles, bare-bulb ceiling light fixtures, tar-impregnated cotton sleeves) and upgraded in the 1940s or 1950s. (knotty-pine finished basement, 12-circuit fuseboxes)
    Is this house Downriver, or possibly in Dearborn? I do most of my work in Livonia, and most homes are built in 1950 or later. It's the 1950-56 ones that have the problem with wiring lacking an EGC.