    transfomer: why overcurrent protection is not required on the grounded conductors?

    I just want to know why OP is not required on the grounded conductors?

  2. #2
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    23,723
    Because it's controllable, and if it were to open independently, could cause over-voltages.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  3. #3
    Join Date
    Apr 2016
    Location
    Georgia
    Posts
    520
    Quote Originally Posted by dawsez View Post
    I just want to know why OP is not required on the grounded conductors?
    Unless you have a shared neutral between phases (not advisable), you should never have current on the neutral once the phase conductor of the circuit has been interrupted, i.e. CB opened/tripped. IEC is different - they use two pole CB's to interrupt both phase (hot) and neutral on single phase branch circuits.

  4. #4
    Join Date
    Jan 2011
    Location
    United States
    Posts
    8,126
    What application do you have in mind? Above 600 volts is not uncommon for the neutral to have CTs for measuring current.