What size diesel generator would be needed to stagger start and run (2) 50HP motors? Reference uploaded motor nameplate. We have a 100kW geneator that does fine starting and running a single motor, however, when we attempt to start the second motor the motor already running quits running :?. Any general guidelines for sizing generators for electric motors?

Thanks,
 

Attachments

  • 50HP_Motor.jpg
    50HP_Motor.jpg
    144 KB · Views: 1
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Try to find a different source for the control voltage. That is what was dropping out on a large motor we had to start with a generator a few years ago. We told them one start a day and leave the sucker running, loaded or not.

Best solution is a properly sized Genset.

Duh that's good, huh? Tell you to do what you already know you need to do.:slaphead:

We had a small one sized recently for a submersible well. Well mfg suggested the gen itself be sized 2 times the KVA of the motor.
 
Last edited:

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Quick rule of thumb:
kW of generator = 3X the HP, if you want the VD to be less than 5% on startup. You are at 2X with one motor, so your VD is already likely more than 5% at startup, but not enough to cause your starter coil to drop out. But when you start the 2nd motor, it is. That's why using a separate control power source would likely allow that generator to work, but putting a UPS on it might work too.

If you are OK with upping the size of the genset, I would go with 150kW, because knowing that one starts with 100kW, the first motor is going to consume the first 50kW after it is running, so you will have 100kW left over and you already know that worked for you.
 

mayanees

Senior Member
Location
Westminster, MD
Occupation
Electrical Engineer and Master Electrician
Quick rule of thumb:
kW of generator = 3X the HP, if you want the VD to be less than 5% on startup. .

.. with all due respect Jraef, I submit that the 5% number would apply to the running voltage drop (VD), which would be consistent with NEC 695.7 that allows 15% starting VD and 5% for 115% of fla - for fire pumps. I do agree with the 3X number...
 