Thread: Residential dead panel alterations

  1. #1
    Join Date
    Jul 2018
    Location
    Brooklyn, NY
    Posts
    1

    Residential dead panel alterations

    During a recent inspection, I encountered a residential dead panel that had additional fasteners added to the inside of the live portion of the breaker panel. I know that alterations above and beyond the manufactured engineered specifications should not be made. Is there a specific NEC ruling on this. Beyond the obvious, I'd like to be specific when my client asks why this shouldn't be done.
    Attached Images Attached Images  

  2. #2
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,816
    I would want to see the inside before I said you can't do that.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)

  3. #3
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Quote Originally Posted by don_resqcapt19 View Post
    I would want to see the inside before I said you can't do that.
    Yes I agree.

    What truly stumps me is why that hardware could be there in the first place.

    I am having a bad vision of a CPT, relay, or such bolted to the cover!
    "Electricity is really just organized lightning." George Carlin


    Derek

  4. #4
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    23,703
    To me, they seem extremely symmetrical, as if original.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  5. #5
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    1,840
    Similar alterations would be made if one was installing a listed generator interlock.

  6. #6
    Join Date
    Feb 2003
    Location
    Minnesota
    Posts
    6,954
    Quote Originally Posted by Homemedic View Post
    . . . I know that alterations above and beyond the manufactured engineered specifications should not be made. Is there a specific NEC ruling on this. Beyond the obvious, I'd like to be specific when my client asks why this shouldn't be done.
    Did you photo the other side of the deadfront? If a picture is worth a thousand words, I'd say we're missing another thousand or so words that complete the Story.
    Another Al in Minnesota

  7. #7
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Quote Originally Posted by LarryFine View Post
    To me, they seem extremely symmetrical, as if original.
    Ugh!

    Was not paying attention. Missed the plural hardware reference and did not even see the lower right hand side of pic.

    Just saw that hardware in the upper left and thought “huh?”.
    "Electricity is really just organized lightning." George Carlin


    Derek

  8. #8
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    23,703
    Quote Originally Posted by Coppersmith View Post
    Similar alterations would be made if one was installing a listed generator interlock.
    Not to mention putting new guts and cover on an existing enclosure, which I've done more than once.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  9. #9
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,500
    Quote Originally Posted by LarryFine View Post
    To me, they seem extremely symmetrical, as if original.
    I agree, hardware that is present may not be original, but something may have been there and this is just plugging holes now.

    It amazes me how many think it is taboo to modify a loadcenter cabinet in any way. If that is what one feels then we may as well throw away KO punches and drilling bits. And how are you supposed to enter some cabinets that you order with no pre formed KO's at all?
    I live for today, I'm just a day behind.

  10. #10
    Join Date
    Aug 2009
    Location
    Central NC
    Posts
    1,908
    That just looks like the dead front retaining screws to me, though different from what I've usually seen. I actually like screws coming through to place cover on them. Then you put nut on and don't have to maneuver a screw into the panel and try to hit right angle.