Do I really use 14.3KW for the range load for the optional Calculation since name plate data is suppose to be used?
The manufacturer's data is as follows: 240V, 1 phase, 14.3KW. Minimum Circuit Required: 40A.
14.3KW at 240V is 59.58Amps. Obviously, 40A will limit this amount load.
(I thought this was a typo, but i noticed other manufacturer also have similar kw ratings and circuit sizing).
With this, Do I really use 14.3KW for the optional Calculation since this is the name plate? Does not make sense.
Would appreciate you opinion.
rodma808
The manufacturer's data is as follows: 240V, 1 phase, 14.3KW. Minimum Circuit Required: 40A.
14.3KW at 240V is 59.58Amps. Obviously, 40A will limit this amount load.
(I thought this was a typo, but i noticed other manufacturer also have similar kw ratings and circuit sizing).
With this, Do I really use 14.3KW for the optional Calculation since this is the name plate? Does not make sense.
Would appreciate you opinion.