    Pool Bonding Question

    I am currently working on a pool that the Builder hooked up the equippotential Bond to the house service main grounding electrode via #8 bare copper. However the House service panel is about five to six feet from the edge of coping from the pool. Very old pool and house. the grounding electrode fell within the perimeter of the pool therefore he felt it should be attached. Is this an issue? Or should I detach the gec connected to the grounding electrode and drive a new rod establishing a new grounding system for the service? Thanks.

  2. #2
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,640
    Pools and gas stations are the two most uncommented topics. I don't think you need to detach anything and I would not drive any new ground rods.
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.

  3. #3
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,030
    Quote Originally Posted by ActionDave View Post
    Pools and gas stations are the two most uncommented topics.
    Uncommented topics????

    Lack of comments...

    Undocumented code...

    Not sure what you mean. Two definitions.
    "Electricity is really just organized lightning." George Carlin


    Derek

  4. #4
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,440
    Quote Originally Posted by Elky57 View Post
    I am currently working on a pool that the Builder hooked up the equippotential Bond to the house service main grounding electrode via #8 bare copper. However the House service panel is about five to six feet from the edge of coping from the pool. Very old pool and house. the grounding electrode fell within the perimeter of the pool therefore he felt it should be attached. Is this an issue? Or should I detach the gec connected to the grounding electrode and drive a new rod establishing a new grounding system for the service? Thanks.
    There is not alot of info here so I will take a shot at it. I assume the equipotential bonding connects to the pool pump????? If so there is a connection thru the equipment grounding conductor to the main service which in turn is connected to the ground rod. Probably not an issue.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  5. #5
    Join Date
    Mar 2014
    Location
    McKinney, Texas
    Posts
    1,386
    Quote Originally Posted by Elky57 View Post
    I am currently working on a pool that the Builder hooked up the equippotential Bond to the house service main grounding electrode via #8 bare copper. However the House service panel is about five to six feet from the edge of coping from the pool. Very old pool and house. the grounding electrode fell within the perimeter of the pool therefore he felt it should be attached. Is this an issue? Or should I detach the gec connected to the grounding electrode and drive a new rod establishing a new grounding system for the service? Thanks.
    Greetings,

    I will simply address the issue of the EBG connected to the dwellings GE. It is permitted to be done as described in 680.26(B) but not required.

    "An 8 AWG or larger solid copper bonding conductor provided to reduce voltage gradients in the pool area shall not be required to be extended or attached to remote panelboards, service equipment, or electrodes."

    Paul W. Abernathy
    Electrical Code Academy, Inc.
    CMP #5 and #17
    *All code responses are based on the 2017 National Electrical Code[NEC]

  6. #6
    Join Date
    Feb 2003
    Location
    Pennsylvania
    Posts
    2,466
    Quote Originally Posted by Elky57 View Post
    the grounding electrode fell within the perimeter of the pool
    Quote Originally Posted by MasterTheNEC View Post
    Greetings,

    I will simply address the issue of the EBG connected to the dwellings GE. It is permitted to be done as described in 680.26(B) but not required.

    680.26 Equipotential Bonding.
    B (7) Metal Wiring Methods and Equipment. Metal-sheathed cables and raceways, metal piping, and all fixed metal parts shall be bonded.

    I agree with Dennis since the bonding is required to be connected to the source equipment grounding system there is no concern

    The OP question seems to indicate that the rod is driven 5 ft or less from the water edge of the pool. The question seems to be is this rod installed in the perimeter of the pool required to be bonded

    I would say yes