    Quote Originally Posted by electrofelon View Post
    You have a feeder, it is a feeder tap.
    240.21(B) "Conductors shall be permitted to be tapped, without overcurrent protection at the tap, to a feeder as specified in....".

    I have conductors tapped to load side of fused service disconnect terminals not feeders. How does 240.21(B) apply?

    Sent from my SM-G935U using Tapatalk

  2. #12
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,818
    Quote Originally Posted by hhsting View Post
    240.21(B) "Conductors shall be permitted to be tapped, without overcurrent protection at the tap, to a feeder as specified in....".

    I have conductors tapped to load side of fused service disconnect terminals not feeders. How does 240.21(B) apply?

    Sent from my SM-G935U using Tapatalk
    There was a proposal to add language stating that a feeder tap may start at the load terminals of a device, but it was rejected as being Un necessary. You dont actually need a wire type feeder to make a feeder tap.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  3. #13
    Join Date
    May 2011
    Posts
    4,690
    Quote Originally Posted by hhsting View Post
    240.21(B) "Conductors shall be permitted to be tapped, without overcurrent protection at the tap, to a feeder as specified in....".

    I have conductors tapped to load side of fused service disconnect terminals not feeders. How does 240.21(B) apply?

    Sent from my SM-G935U using Tapatalk
    Look at the definition of a tap conductor. Both sets of conductors on the load side of your disconnect meet the definition.