    class i division 1 group d

    Class 1 division 1 im familiar with this is regarding a acetone recycler placed out side a paint booth area the equipment is class 1 div 1 and group D I am not familiar with group D requirements I do know im trying to keep my disconnect out of my class area for obvious reasons. SO what is the group D ?

  2. #2
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,998
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    500.6(A)(4)
    Bob

  3. #3
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    5,253
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    See Section 500.6(A)(4). You also should review NFPA 497 as referenced in the Informational Note to obtain the “T-Code” required in Sections 500.8(B) and (C)(4).
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  4. #4
    Join Date
    Jul 2017
    Location
    Alberta, Canada
    Posts
    42
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Group A = Acetylene
    Group B = Hydrogen (and similar)
    Group C = Ethylene (and similar)
    Group D = Propane (and similar)

    Group D often means the location has methane or propane.