Thread: Service grounding

  1. #11
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    14,978
    Quote Originally Posted by petersonra View Post
    There is only one GEC. The other wires are bonding conductors.
    Disagree. 2 GECs and 1 bonding jumper.

    Meter to rod. GEC
    Rod to rod . Jumper.

    Panel to water. GEC.
    "Electricity is really just organized lightning." George Carlin


    Derek

  2. #12
    Join Date
    Nov 2008
    Location
    Iowa
    Posts
    44

    gas pipe

    Adding to this thread, if in the original OP's situation with two ground rods and an GEC to a metal water pipe system can a metal gas piping system in the same house be bonded to a water pipe with #6 copper or does the #6 copper have to go all the way back to the main panel and be bonded there? In any case is this #6 copper a GEC or an EGC?

  3. #13
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    14,978
    Quote Originally Posted by trojans4 View Post
    Adding to this thread, if in the original OP's situation with two ground rods and an GEC to a metal water pipe system can a metal gas piping system in the same house be bonded to a water pipe with #6 copper or does the #6 copper have to go all the way back to the main panel and be bonded there? In any case is this #6 copper a GEC or an EGC?
    A gas pipe is never an electrode. So, no GEC.

    Gas lines may be bonded through an EGC or a bonding jumper. See 250.104(B)

    Article on gas lines and bonding.https://www.ecmag.com/section/codes-...ing-gas-piping
    "Electricity is really just organized lightning." George Carlin


    Derek

  4. #14
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,608
    Quote Originally Posted by trojans4 View Post
    Adding to this thread, if in the original OP's situation with two ground rods and an GEC to a metal water pipe system can a metal gas piping system in the same house be bonded to a water pipe with #6 copper or does the #6 copper have to go all the way back to the main panel and be bonded there? In any case is this #6 copper a GEC or an EGC?
    Sounds like a bonding jumper. If this is CSST some places require that it be bonded otherwise as Jumper stated no additional gas pipe bond is required if it's black gas pipe.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  5. #15
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    37,529
    Quote Originally Posted by jumper View Post
    I should have said uncommon IME instead of unconventional maybe. Few POCOs I have worked with allow me to use the meter base.
    Quote Originally Posted by infinity View Post
    Must be a regional thing, around here the connection is not permitted in the meter enclosure by the POCO but I have seen this commonly elsewhere in the country.
    We have a POCO around here that wants a ground rod connected to the meter enclosure regardless of whatever electrodes you may have connected elsewhere.
    I live for today, I'm just a day behind.

  6. #16
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    14,978
    Quote Originally Posted by kwired View Post
    We have a POCO around here that wants a ground rod connected to the meter enclosure regardless of whatever electrodes you may have connected elsewhere.
    No harm IMO. Just unneeded cost and labor.
    "Electricity is really just organized lightning." George Carlin


    Derek

  7. #17
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    37,529
    Quote Originally Posted by jumper View Post
    No harm IMO. Just unneeded cost and labor.
    I agree. They can refuse to energize if you don't meet their requirements.
    I live for today, I'm just a day behind.