Is it bonded?

Status
Not open for further replies.

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
Product Series GP15000E
Model (Configuration) 5734-1 (EPA/49-State)
AC Rated Output Running Watts: 15000
AC Maximum Output Motor Starting Watts: 22500
AC Voltage 120/240 VAC
AC Frequency 60 Hz
Rated VAC Amperage 125/62.5
Max Rated VAC Amperage 187.8/93.75
Engine Displacement 992cc
Engine Type OHVI
Engine RPM 3600
Recommended Oil 10W-30 / SAE30
Lubrication Method Oil Pump
Automatic Voltage Regulation (AVR) Yes
Oil Filter Yes - Spin On
Choke Location On Engine
Fuel Shut Off On Fuel Tank
Starting Method Electric
Low Oil Shutdown Method Low Pressure
Battery Type Group U1, 360 CCA
Neutral Bonded to Ground No - Floating Neutral
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
side note: don't you love the way that model goes to full throttle immediately on starting ?..got be rough on the wearing surfaces
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Product Series GP15000E
Model (Configuration) 5734-1 (EPA/49-State)
AC Rated Output Running Watts: 15000
AC Maximum Output Motor Starting Watts: 22500
AC Voltage 120/240 VAC
AC Frequency 60 Hz
Rated VAC Amperage 125/62.5
Max Rated VAC Amperage 187.8/93.75
Engine Displacement 992cc
Engine Type OHVI
Engine RPM 3600
Recommended Oil 10W-30 / SAE30
Lubrication Method Oil Pump
Automatic Voltage Regulation (AVR) Yes
Oil Filter Yes - Spin On
Choke Location On Engine
Fuel Shut Off On Fuel Tank
Starting Method Electric
Low Oil Shutdown Method Low Pressure
Battery Type Group U1, 360 CCA
Neutral Bonded to Ground No - Floating Neutral

Thank you. Now to find out why, or what happened.
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
To bond, or Not to bond.

To bond, or Not to bond.

The gen is mounted in the back of a pickup. 4 wire cord is run via the 50 amp recept to a work trailer containing a small panel with MCB. Neutral isolated. EG is bonded to frame of truck and frame of trailer.

Bonding neutral at panel in trailer seems like the correction. What am I missing?
 

kwired

Electron manager
Location
NE Nebraska
The gen is mounted in the back of a pickup. 4 wire cord is run via the 50 amp recept to a work trailer containing a small panel with MCB. Neutral isolated. EG is bonded to frame of truck and frame of trailer.

Bonding neutral at panel in trailer seems like the correction. What am I missing?
I'd say leave it as is.

If you bond neutral to ground in the trailer and then sometime plug trailer into a premises wiring system you potentially introduce more problems there with a unnecessary neutral-ground bond then if leaving it float while on the generator. JMO.

Having this supply ungrounded isn't as much of a problem as some want to think it is. Keeping the grounding/bonding properly intact from the utility supplied source that is grounded is important though.
 