    Two Services for one building

    I am working on a project that has two existing buildings (lets say building A and B) with their own services. The service for building A has maxed out but there is available capacity in the Main distribution board fed by Service for Building B. I know NEC only allows one service for one building (unless for exceptions stated) but I would like to know if there is a way I would be able to feed a load in building A from the Main distribution board in building B?

  2. #2
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,030
    Not in any way that I think of.

    Unless this is a supervised industrial place, then maybe. IDK.
    "Electricity is really just organized lightning." George Carlin


    Derek

  3. #3
    Join Date
    May 2018
    Location
    Jamaica and london
    Posts
    347
    The one service per building... is that all buildings or is multiple dwelling different?
    Jamaica Utilities want the runs from the meter boxes up the meter pole separate for each meter to a location... and kept separate to the panels inside, of course. So, a few houses I have seen have a spaghetti nest at the top of the meter pole, since some people have as many as eight apartments in their homes. I always thought it would be better to do like in USA with one run to the pole and the bus system I see but...The Jamaican attitude is, it is easier to steal electricity if a bus system is used...
    still think it more dangerous their way..lol..

  4. #4
    Join Date
    Feb 2003
    Location
    Seattle, WA
    Posts
    19,048
    This might be more tricky than you would expect.

    230.6 says one service per building, and I don't think any of the "unless permitted by" statements apply to your situation.
    225.30 says one outside feeder per building, and I don't think any of the "unless permitted by" statements apply to your situation.

    However, you are not suggesting more than one service or more than one feeder. Rather, you are suggesting one of each. I don't think the code language, as written, forbids this. I suspect that the "one of each" installation is not in compliance with the intent of the code authors. But it is not in violation of the language they put into the code.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.

  5. #5
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,531
    Quote Originally Posted by charlie b View Post
    This might be more tricky than you would expect.

    230.6 says one service per building, and I don't think any of the "unless permitted by" statements apply to your situation.
    225.30 says one outside feeder per building, and I don't think any of the "unless permitted by" statements apply to your situation.

    However, you are not suggesting more than one service or more than one feeder. Rather, you are suggesting one of each. I don't think the code language, as written, forbids this. I suspect that the "one of each" installation is not in compliance with the intent of the code authors. But it is not in violation of the language they put into the code.
    That is what I was thinking but I didn't want to comment without first checking the language. The code seems to want "one supply" but the combination of one service and one feeder doesn't seem to be specifically prohibited.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  6. #6
    Join Date
    Feb 2003
    Location
    Pennsylvania
    Posts
    2,466
    Quote Originally Posted by charlie b View Post
    This might be more tricky than you would expect.

    230.6 says one service per building, and I don't think any of the "unless permitted by" statements apply to your situation.
    225.30 says one outside feeder per building, and I don't think any of the "unless permitted by" statements apply to your situation.

    However, you are not suggesting more than one service or more than one feeder. Rather, you are suggesting one of each. I don't think the code language, as written, forbids this. I suspect that the "one of each" installation is not in compliance with the intent of the code authors. But it is not in violation of the language they put into the code.
    Quote Originally Posted by electrofelon View Post
    That is what I was thinking but I didn't want to comment without first checking the language. The code seems to want "one supply" but the combination of one service and one feeder doesn't seem to be specifically prohibited.
    I’m sorry but I completely disagree with this concept.

    For this concept to be applicable it has to be ignored that the service location is indicated to be at first building or structure and the whole scope of article 225 is branch circuits and feeders to additional buildings or structures.

    Article 225 goes on to say the additional branch circuit or feeder supplies are on the load side of the premise service

    And this all has to be on the same property under single management

    ¬“225.30 Number of Supplies.
    Where more than one building or other structure is on the same property and under single management, each additional building or other structure”

  7. #7
    Join Date
    Feb 2003
    Location
    Pennsylvania
    Posts
    2,466
    Quote Originally Posted by ashenafidemissie View Post
    I am working on a project that has two existing buildings (lets say building A and B) with their own services. The service for building A has maxed out but there is available capacity in the Main distribution board fed by Service for Building B. I know NEC only allows one service for one building (unless for exceptions stated) but I would like to know if there is a way I would be able to feed a load in building A from the Main distribution board in building B?
    My advise to the OP, you have little chance you will get an authority to allow this based on it being expedient , without tying your reason to one from article 230 or 225 and show a good reason to allow any additional supplies to a single building