    PACKAGE SUBSTATION 13.8 KV/220V 3 PHASE WITHOUT MAIN BREAKER AT SECONDARY.

    The package sub station has input 13.8 kv and the sec is 3ph 220 v. The sec does not have main breaker.
    What shall be the short circuit rating of branch breakers.Is there any relation of such rating with the main busbar.

  2. #2
    Join Date
    Feb 2003
    Location
    Seattle, WA
    Posts
    19,047
    You can't calculate the short circuit current without knowing the KVA rating of the transformer and its percent impedance. Do you have that information?
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.

  3. #3
    Join Date
    Jul 2006
    Location
    SE USA as far as you can go
    Posts
    2,666
    If this is truly a packaged substation; i.e. came from one manufacturer as a unit , then they should have taken the short circuit rating of the LV bus into consideration. Regardless, the manufacturer drawings that would have been provided for review and acceptance prior to fabrication would have that information on them and certainly will be on the final drawings shipped with the equipment. The SC rating would be the same as the bus.
    "Just because you're paranoid, doesn't mean they're not out to get you"

  4. #4
    Quote Originally Posted by Anwar Pasha View Post
    The package sub station has input 13.8 kv and the sec is 3ph 220 v. The sec does not have main breaker.
    What shall be the short circuit rating of branch breakers.Is there any relation of such rating with the main busbar.
    The transformers are rated 1000 KVA.

  5. #5
    Join Date
    Jul 2006
    Location
    SE USA as far as you can go
    Posts
    2,666
    Assuming an Impedance of 5.75%;

    In ANSI/IEEE US standard ratings would be 65KA.

    In IEC I believe it would be standard 50KA.
    "Just because you're paranoid, doesn't mean they're not out to get you"

  6. #6
    Join Date
    Jul 2013
    Location
    Resting under the Major Oak UK
    Posts
    1,174
    This is the LV end of a UK packaged substation, there are no busbars to worry about as the manufacturers have type tested them. The maximum fault level would be 45kA, the fused output ways are rated for 80kA.