    When to use Stranded insted of Solid Service bonding

    Is there something in the code book that states after a curtain wire size if going through any wire way that you need to use stranded wire for grounding and bonding? I did a service and used #8 solid for my bonding and grounding from my meter housing to my Panel. I was told that after a curtain wire size it needed to be stranded. But was not told what code reference to use. Any help.

  2. #2
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Code accepts both for grounding, any size. 250.62

    Conductors in raceways max at #10 solid. 310.106.(C)
    "Electricity is really just organized lightning." George Carlin


    Derek

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,366
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I've never used solid for GEC's or bonding jumpers. I've heard of guys running #6 or #4 solid but I just don't get it.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,004
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    I know a wireway is a raceway but it seems ridiculous to call someone on 310.106
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  5. #5
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    I've never used solid for GEC's or bonding jumpers. I've heard of guys running #6 or #4 solid but I just don't get it.
    Quite common in resi, not so much in commercial IME.
    "Electricity is really just organized lightning." George Carlin


    Derek

  6. #6
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,366
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    Quite common in resi, not so much in commercial IME.
    Around just about everyone uses stranded even in residential.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  7. #7
    Join Date
    May 2018
    Location
    Jamaica and london
    Posts
    1,111
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    if you are running in conduits, doesnt it make sense to use stranded even if you are using 16 guage wire? Much less larger sizes? So they bend in the bends rather than scratch off the insulation?

    Or is there a requirement to use solid at certain sizes?

  8. #8
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Adamjamma View Post

    Or is there a requirement to use solid at certain sizes?
    The NEC never mandates solid.
    "Electricity is really just organized lightning." George Carlin


    Derek

  9. #9
    Join Date
    May 2018
    Location
    Jamaica and london
    Posts
    1,111
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thank You.

  10. #10
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,366
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    The NEC never mandates solid.
    I think they do for pools.