    Fuse servicing

    Nec 2014 690.16 has the requirement of providing disconnecting means that isolates fuse for servicing. However, i looked but did not notice 690.16 language for fuse NEC 2017. I maybe incorrect but looks like it was removed. Any idea as to why it was removed?

  2. #2
    Join Date
    Nov 2015
    Location
    CA, USA
    Posts
    706
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It was deleted since the rewrite of 690.15 covers equipment disconnects in general. So it's still required to be able to isolate fuses for replacement.