    Fuse servicing

    Nec 2014 690.16 has the requirement of providing disconnecting means that isolates fuse for servicing. However, i looked but did not notice 690.16 language for fuse NEC 2017. I maybe incorrect but looks like it was removed. Any idea as to why it was removed?

  2. #2
    Join Date
    Nov 2015
    Location
    CA, USA
    Posts
    648
    It was deleted since the rewrite of 690.15 covers equipment disconnects in general. So it's still required to be able to isolate fuses for replacement.