Thread: Connecting UFER to a ground rod

  1. #71
    Join Date
    Sep 2018
    Location
    Evansville
    Posts
    6
    Rob I'm only presuming. I cannot read the insulation.

  2. #72
    Join Date
    Sep 2018
    Location
    Evansville
    Posts
    6
    Roger would we worry about altering the integrity of the cable by stripping it back maybe loosening the wound and ceasing its conductivity?

  3. #73
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,368
    Quote Originally Posted by Frontman4u View Post
    Roger would we worry about altering the integrity of the cable by stripping it back maybe loosening the wound and ceasing its conductivity?
    No.

    Roger
    Moderator

  4. #74
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,160
    Quote Originally Posted by Frontman4u View Post
    Rob I'm only presuming. I cannot read the insulation.
    As Roger stated it can be bare so having insulation of any type would also be permitted. It's not required to be green either, although it's common to use green conductors for bonding jumpers and GEC's.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted