    #8 vs #6 RV Outlet

    I'm installing a 50 amp RV outlet on a power panel. The charts indicate you can use #8 for 50 amp but my co-worker is saying I need #6. The length of wire is less than 5 feet. Comments please.

  2. #2
    Join Date
    Jul 2007
    Location
    Iowegia
    Posts
    17,948
    Not enough information.

    What 'chart'? And what type of wire/cable?

  3. #3
    Join Date
    Nov 2003
    Location
    Roanoke, VA.
    Posts
    4,532
    Quote Originally Posted by TXLAKE View Post
    I'm installing a 50 amp RV outlet on a power panel. The charts indicate you can use #8 for 50 amp but my co-worker is saying I need #6. The length of wire is less than 5 feet. Comments please.
    If the lugs you're connecting to are rated for 75 degrees #8 is good for 50 amps I think, don't have my book in front of me.....
    and as 480 asked what type of wire?
    Sometimes I don't know whether I'm the boxer or the bag.

  4. #4
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,624
    I doubt that the RV outlet has 75° C terminals so your #8 is NG unless you want to pigtail the #8's to #6's at the outlet.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  5. #5
    Join Date
    Jul 2007
    Location
    Iowegia
    Posts
    17,948
    Upon further reflection:

    5 feet? Install 6 and call it a day. How much more would it cost?

  6. #6
    Join Date
    Aug 2018
    Location
    NJ
    Posts
    48
    Use aluminum #6.

  7. #7
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,624
    Quote Originally Posted by KaBoom! View Post
    Use aluminum #6.
    Only good for 40 amp at 60° C.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  8. #8
    Join Date
    Aug 2018
    Location
    NJ
    Posts
    48
    Quote Originally Posted by infinity View Post
    I doubt that the RV outlet has 75° C terminals so your #8 is NG unless you want to pigtail the #8's to #6's at the outlet.
    Quote Originally Posted by infinity View Post
    Only good for 40 amp at 60° C.
    In 20 years I have never seen this flagged. Millions of range and RV outlets are done this way, etc.

  9. #9
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,624
    Quote Originally Posted by KaBoom! View Post
    In 20 years I have never seen this flagged. Millions of range and RV outlets are done this way, etc.
    It's fine if the terminals are rated for 75° C. If not then for 20 years someone has been doing it wrong.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  10. #10
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,442
    I am closing this thread, in accordance with the Forum Rules.
    This site is designed for:
    • Contractors
    • Electricians
    • Engineers
    • Inspectors
    • Instructors
    • Other electrically related individuals

    * This NEC Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.
    If you feel this action to be in error, feel free to contact me via PM to explain.eminder to all members, if you see a questionable post, feel free to report it by clicking the button at the bottom left corner of the post.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •