Thread: 2 - 20 circuit loadcenters on 1 100amp breaker

  1. #1

    2 - 20 circuit loadcenters on 1 100amp breaker

    i have a 100amp single phase main breakers feeding 1- 20 circuit panel ,, and from that panel i have a 90mp breaker feeding another 100amp 20 circuit panel .
    is this code complaint ? i cant find anything prohibits this .

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,152
    Yes code complaint.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    I agree with Infinity.

    100A main, 90A sub......SER to sub?
    "Electricity is really just organized lightning." George Carlin


    Derek

  4. #4
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,500
    Second panel is now effectively a 90 amp panel, even if it had a 200 amp main breaker in it.