User Tag List
Page 3 of 3 FirstFirst 1 2 3
Results 21 to 22 of 22
Thread: multiple current carrying conductors in a single racway (loading the boat)
  1. #21
    Join Date
    Mar 2003
    Vermont
    Posts
    2,030
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    well yes....
    Depending on distance , many main runs may be designed as #10's
    ~RJ~
  2. #22
    Join Date
    Dec 2011
    Ocala, Florida, USA
    Posts
    2,997
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by follybeacher View Post
    My question is a high level estimating question, not a granular engineering question. I understand how to calculate available fill per Ch. 9 perform adjustment factors per 310.15(B)(2)(a). When required to perform these calcs, I do so. That's not the question...
    The question is what rules can an estimator most always apply to reduce cost in regards to 'loading the boat'? I build receptacle assemblies with an average conduit length to reach a 4sq box. Then I group 3 together and sending them to the respective panel. My rule (which I'm trying to expand on) is always using 3 ckts per homerun.
    Can I apply other rules without having to perform engineering calcs? Time is short these days and I want to be as competitive as code compliantly possible.
    I made a quick sketch to show you what's in a typical assembly and the 4sq/homerun I'm wheeling off. (This sketch is drawn as if they're dedicated ckts )
    Attachment 21041
    The bottom line is that every estimate is unique. In a standard office situation with MC allowed, 15 feet of MC with every receptacle assembly, 12 feet of 12-3 for every switch, 10 feet for every light fixture and I roll the 3 way witches and put a 12-3 in between them. Then I use 3 circuits per home run just like you. If I want to get a little lower, I will use 4 home runs in a conduit which is still allowed. Home runs can be in the slab in PVC to get lower. But I usually use three. I run the home run to about the center of the three circuits use a box and I am done. The problem is when your receptacle density changes or you want to be as low as possible. Also if you are using conduit no MC allowed. I have been doing it for years and if I want any accuracy in my estimate, I just roll it. For conduit I will sketch out a run and roll. I set an add for 8 feet (assume 9 foot ceiling) and add 8 plus eight for any run that jumps two walls or a door. I don't add for receptacles on the same wall or an adjacent wall. But it takes time.
    I know what I don't know, and I know where to go to find it!
Posting Permissions
  • You may not post replies
  • You may not edit your posts