    When our technicians need to replace 120 volt devices such as temperature or pressure switches; our policy for this job is to always work de-energized. To de-energize these devices they must go to a control cabinet with 120 volt exposed live parts and pull a small swing out control fuse.
    The first option of 70E is to not work energized if you don’t have to and if you must work energized you usually need a permit. However, though one would still need PPE, 70E does not require a permit for investigating, testing or troubleshooting, etc..
    In this case our goal is to work de-energized downstream from this panel by pulling a little control fuse.
    So, all that said, is the act of pulling this fuse so we can work de-energized, Permit Required Energized Work?
  2. #2
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,494
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by DCS View Post
    Technically, yes, but if it opens like a switch, I wouldn't bother.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  3. #3
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,283
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    the act of then checking where you will be working to make sure you opened the right fuse is also energized work.
    Bob
  4. #4
    Join Date
    Feb 2005
    Charlotte, NC
    Posts
    6,812
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Technically yes, but what you can do for something like this is to develop a "standing" work permit for this specific task. Post it, renew it annually. You don't have to issue a new permit everytime you do this.
  5. #5
    Join Date
    Jul 2006
    Posts
    8,382
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    So does the control panel have ONLY 120V parts in it? If so, the incident energy will likely be so low that the PPE required (1?) would be just what should be standard attire for electricians nowadays; Arc Resistant long sleeve cotton shirt and pants, safety glasses, leather shoes, leather gloves, ear plugs.