NFPA 70E Question MCCs

Status
Not open for further replies.

mikecj

Member
Guys,

NFPA 70E Table 130.7(C)(15)(A)(b) provide arc flash PPE categories for various equipment. For motor control centers there are two entries

600-V class motor control centers (MCCs) - Parameters: Maximum of 65 kA short-circuit current available; maximum of 0.03 sec (2 cycles) fault clearing time; working distance 455 mm (18 in.) Arc flash PPE Category - 2, Arc flash boundary 5 feet

AND

600-V class motor control centers (MCCs) - Parameters: Maximum of 42 kA short-circuit current available; maximum of 0.33 sec (20 cycles) fault clearing time; working distance 455 mm (18 in.) Arc flash PPE Category - 4, Arc flash boundary 14 feet

So am I correct in assuming that the lower the short circuit current or the longer the clearing time, the more hazardous the situation?

Be gentle. I'm a chemical safety guy trying to figure electricity :happysad:

Thanks,

MikeCJ
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Generally yes
Actually the higher the short circuit current the higher the danger as long as the clearing time remains the same.
There is a seeming paradox in that if the fault current (not the short circuit current) goes low enough it can get into a region where a decrease in the current can delay the clearing long enough that the total energy is higher.
 