    Pika Islanding inverter

    Is anyone using the Pika system ? If so, how do i parallel the 7.6 inverters to harvest more power ?
    Also, why is 7.6Kw such a popular inverter size when using batt back up (ie : Storedge)
    Thanks

  2. #2
    Join Date
    May 2011
    Posts
    4,577
    7.6kW is a popular inverter size because a 32A*12.5=40A, and that is the maximum current allowed on a 200A panelboard with a 200A main breaker.