Thread: Sewer Lift Station

  1. #11
    Join Date
    Mar 2014
    Location
    South Florida
    Posts
    298
    Quote Originally Posted by gadfly56 View Post
    I note that the qualifier "with a roof" is part of the definition of "enclosed" and "not enclosed". My claim is you don't have a roof.
    how would hydrogen sulfide be dispersed? it is heavier than air and will collect within the walls without any form of ventilation. to me the "house" is now a confined space, an extension of the wet well. anyone entering it should have a sniffer before they walk in.

  2. #12
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,198
    Quote Originally Posted by drktmplr12 View Post
    how would hydrogen sulfide be dispersed? it is heavier than air and will collect within the walls without any form of ventilation. to me the "house" is now a confined space, an extension of the wet well. anyone entering it should have a sniffer before they walk in.
    Diffusion is your friend. Heavier than air gases only "settle" when they have no way of escaping. It would depend on how many lbm/hr you were generating as to whether you could accumulate any concentration of interest. That in turn would depend on the open roof area as well as local wind speed or lack thereof. This would be an interesting field exercise for some ChemE students.

  3. #13
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    5,246

    The relevant definitions:

    Enclosed Space. The interior space of any tank or unit process that is closed to the atmosphere, excluding vents or pressure relief, or the area around any open tank of unit process surrounded by a building or other structure constructed with a roof and solid walls.

    Not Enclosed. Any tank or unit process open to the atmosphere or the area around any open tank or unit process housed in a building or other structure constructed with a roof and having at least 50% of the wall area open to the atmosphere. Fixed open louvered panels with effective openings greater than 50 percent of the wall area and evenly distributed over the wall area are considered open to the atmosphere.

    NEC 500.5(B)(1) Class I, Division 1. A Class I, Division 1 location is a location
    (I) In which ignitible concentrations of flammable gases, flammable liquid-produced vapors, or combustible liquid-produced vapors can exist under normal operating conditions,
    As I mentioned in my initial response this is an either/or situation. It is either an Enclosed Space or Not Enclosed. While a "roof" is mentioned in both OP definitions, without 50% open walls, it is not Not Enclosed and Enclosed Space is the only other option. This is especially true without sufficient identifiable ventilation. The Enclosed Space definition is not exhaustive and, in fact, mentions a few cases where a roof is not essential.

    A Class I, Division 1 location only requires that ignitible concentrations can exist under normal operating conditions. It doesn't require it to be a constant presence, for long periods of time, or even frequent,

    Most sewer gases are under constant generation. In the OP case, "dispersion" is not relevant. Note it is not mentioned in any of the definitions above while a minimal ventilation is hinted at for the OP definitions.

    I would have no problem defending my classification position for the OP installation in court for both safety and cost-effectiveness. Considering it Not Enclosed is not defensible.

    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  4. #14
    Join Date
    Jun 2013
    Location
    Florida
    Posts
    12
    Thanks for all the input. The structure is a house without a complete roof; block and stucco construction. I feel the space is not "not enclosed" so the prudent approach is to classify the space. I can just also see where I may get some push-back as the space does not meet the letter of the law for enclosed either.

    My co-worker mechanical engineer said that he would need to provide supply and exhaust fans, along with supply and exhaust ductwork, to prevent short cycling from the open roof and properly ventilate the space. The lift station is literally feet away from other houses on each side, so I doubt the neighbors would appreciated the fans running 24/7 right outside their bedroom windows. On top of that, ventilation can only reduce the classification to Class I Div 2, not eliminate it.

    My concerns are for both methane and sulfides, so a combination of heavier and lighter than air.

  5. #15
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,500
    Quote Originally Posted by Bwas View Post
    I have a project that includes a new sewer lift station that pumps both residential and commercial waste water. The wet well has a vent that terminates about a foot above grade and there is a hatch for access to pumping/control equipment in the wet well. The lift station is in a residential area and the owner wants to disguise it. There will be a structure around the wet well that looks like a house; however the roof only extends about three feet inside the footprint of the structure (if you stand on the wet well hatch and look up you see sky). There are no louvers or fans.

    I believe this falls under NFPA 820 table 4.2.2 row 19 which is a pump station that is not physically separated from the wet well, which would require the entire area inside the structure to be Class I Div 1. The trouble I am having is that the structure does not really meet the definition of "enclosed space" or "not enclosed." I am concerned that there is no way for any gasses to dissipate within the structure.

    Any thoughts?

    Enclosed Space. The interior space of any tank or unit process that is closed to the atmosphere, excluding vents or pressure relief, or the area around any open tank of unit process surrounded by a builidng or other structure constructed with a roof and solid walls.

    Not Enclosed. Any tank or unit process open to the atmosphere or the area around any open tank or unit process housed in a building or other structure constructed with a roof and having at least 50% of the wall area open to the atmosphere. Fixed open louvered panels with effective openings greater than 50 percent of the wall area and evenly distributed over the wall area are considered open to the atmosphere.
    Why not extend this vent to outside the structure? It looks like a house, typical house has sewer vents so that shouldn't look out of place. Then you don't have open vent within the space to be concerned about.
    I live for today, I'm just a day behind.

  6. #16
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    5,246
    Quote Originally Posted by kwired View Post
    Why not extend this vent to outside the structure? It looks like a house, typical house has sewer vents so that shouldn't look out of place. Then you don't have open vent within the space to be concerned about.
    This is an excellent recommendation.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  7. #17
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,745
    Quote Originally Posted by kwired View Post
    Why not extend this vent to outside the structure? It looks like a house, typical house has sewer vents so that shouldn't look out of place. Then you don't have open vent within the space to be concerned about.
    And presumably whenever the hatch is open for maintenance a door or other substantial part of the wall is open?

  8. #18
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,198
    Quote Originally Posted by rbalex View Post

    The relevant definitions:


    As I mentioned in my initial response this is an either/or situation. It is either an Enclosed Space or Not Enclosed. While a "roof" is mentioned in both OP definitions, without 50% open walls, it is not Not Enclosed and Enclosed Space is the only other option. This is especially true without sufficient identifiable ventilation. The Enclosed Space definition is not exhaustive and, in fact, mentions a few cases where a roof is not essential.

    A Class I, Division 1 location only requires that ignitible concentrations can exist under normal operating conditions. It doesn't require it to be a constant presence, for long periods of time, or even frequent,

    Most sewer gases are under constant generation. In the OP case, "dispersion" is not relevant. Note it is not mentioned in any of the definitions above while a minimal ventilation is hinted at for the OP definitions.

    I would have no problem defending my classification position for the OP installation in court for both safety and cost-effectiveness. Considering it Not Enclosed is not defensible.

    OK, I can accept that argument.

  9. #19
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    5,246
    Quote Originally Posted by GoldDigger View Post
    And presumably whenever the hatch is open for maintenance a door or other substantial part of the wall is open?
    It would need to be worked under a confined space and possibility a hot work permit but that would be true in any case.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  10. #20
    Join Date
    Oct 2013
    Location
    MD
    Posts
    73
    Quote Originally Posted by kwired View Post
    Why not extend this vent to outside the structure? It looks like a house, typical house has sewer vents so that shouldn't look out of place. Then you don't have open vent within the space to be concerned about.
    NFPA 820 Annex has a figure showing exactly this. The house with a hatch in it is still the same rating as the wet well. Wet Well and house would have to be 'physically separated' to be unclassified. Physically Separated - A gastight partition between two adjacent spaces, or two nonadjacent spaces, with no means of gas communication between the spaces.