User Tag List
Page 1 of 11 1 2 3 ... LastLast
Results 1 to 10 of 110
Thread: 2020 Fire Fighter Disco 1 & 2 Family Dwellings 230.85
  1. #1
    Join Date
    Feb 2005
    South of Bawstin
    Posts
    1,259
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    New proposed section 230.85 requires a Emergency Disconnect for service conductors of 1 & 2 family dwellings located readily accessible outside the dwelling.
    Know as the "Fire Fighter Disconnected"
    Here is the language...
    230.85 Emergency Disconnects(s)
    For one- and two-family dwelling units, all service conductors shall terminate in disconnecting means having a short-circuit rating equal to or greater than the available fault current, installed in a readily accessible outdoor location. If more than one disconnect is provided, they shall be grouped. Each disconnect shall be one of the following:
    (1) Service disconnect(s) marked as follows: EMERGENCY DISCONNECT, SERVICE DISCONNECT
    (2) Meter disconnect(s) installed per 230.83(#) and marked as follows: EMERGENCY DISCONNECT, METER DISCONNECT, NOT SERVICE EQUIPMENT
    (3) Other than listed disconnect switch(es) or circuit breaker(s) on the supply side of each service disconnect that are suitable for use as service equipment and marked : EMERGENCY DISCONNECT, NOT SERVICE EQUIPMENT
    Markings shall comply with 110.21(B)
  2. #2
    Join Date
    Mar 2003
    Vermont
    Posts
    1,956
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    There's one local poco i work with that's had that policy for years
    and they've a few FF's
    ~RJ~
  3. #3
    Join Date
    May 2018
    Jamaica and london
    Posts
    1,258
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by shortcircuit2 View Post
    I hope it does not go through or requires put in a box that only firefighters can access...
    imagine the burglar scenario... turn off firefighter disconnects for home, no alarm, take time breaking in...
    same with murderers or rapists... turn off firefighters disconnect..no video gear to catch me...lol..
  4. #4
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,633
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I dislike this one. If it were required many would put a big old lock on it anyway.
    Rob
  5. #5
    Join Date
    Feb 2003
    Illinois
    Posts
    23,908
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The PI called for that for all services, but the panel action limited to one and two family dwellings. As a former first responder, I think access to kill the power to commercial is more critical than for one and two family dwellings, especially since some utilities remotely kill the power on a call from the FD where the dwelling units have smart meters
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)
  6. #6
    Join Date
    Dec 2011
    Wisconsin
    Posts
    564
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by don_resqcapt19 View Post
    We have smart meters here, but it is my understanding that they do not have contactors in them and they cannot be shut off remotely. At least that is the way it is here. The larger the service the less likely it is that it can be shut off remotely due the the cost of a contactor.
  7. #7
    Join Date
    Feb 2007
    USA
    Posts
    5,808
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by packersparky View Post
    Well smart meters can have a internal disco. It may be a option though.
  8. #8
    Join Date
    Dec 2011
    Wisconsin
    Posts
    564
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Sierrasparky View Post
    I understand that they can have a contactor, but around here they do not. They cannot be disconnected remotely.
  9. #9
    Join Date
    May 2018
    Jamaica and london
    Posts
    1,258
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thought of using a box like utilities use here in UK to limit number of people can access the box but the keys are so common that you still end up with thieves having access to the disconnects to break into the property easier...
    is the reasoning simply imply to reduce the problems of the solar backfeeds? Or is it to fully disconnect? Because with the different backfeed methods combined with smart meters and properties like I deal with in Jamaica, can see real problems in the disconnects being in one accessible spot unless we now require the panels to be on an outside wall... disconnects on outside of that wall, panel on inside of that wall...
    really watching this stuff as most properties in Jamaica are setup more like trailers than US homes, with the meter on the property line and an underground usually run to building to an inside panel box... though sometimes run overhead.. older homes have meters on building but POCO requiring meters at property lines due to theft and dogs..lol...
  10. #10
    Join Date
    Mar 2003
    Vermont
    Posts
    1,956
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I use meter/mains when i can.
    It's a safer and better job, jmho
    consider how 408.3 (2) (2017) factors in
    (2) Service Panelboards, Switchboards, and Switchgear. Barri‐
    ers shall be placed in all service panelboards, switchboards, and
    switchgear such that no uninsulated, ungrounded service
    busbar or service terminal is exposed to inadvertent contact by
    persons or maintenance equipment while servicing load termi‐
    nations.
    ~RJ~
Posting Permissions
  • You may not post replies