Thread: Mounting Components on a Type Z Purged Enclosure

  1. #11
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,931
    it wouldn't have created any hazard to pressurize the box one of the panel views was in that was deemed unsuitable for pressurization. Either the keyboard or the touch screen would have just eventually failed but presumably not in some way that would cause some hazard.

    in fact now that I think about it they actually had some terminals that were specifically stated suitable for pressurization.
    Bob

  2. #12
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    5,238
    Quote Originally Posted by petersonra View Post
    it wouldn't have created any hazard to pressurize the box one of the panel views was in that was deemed unsuitable for pressurization. Either the keyboard or the touch screen would have just eventually failed but presumably not in some way that would cause some hazard.

    in fact now that I think about it they actually had some terminals that were specifically stated suitable for pressurization.
    That sounds reasonable. The truth is, while our control systems or electrical engineers may have specified a Type Z system, in my experience, we would have left it up to the panel fabricator to select the touchscreen and not worried about it. Unlike many current CSI type specs, unless there was a specific need, we rarely specified a brand or catalog number, only a performance requirement.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  3. #13
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,931
    Name:  Capture.JPG
Views: 41
Size:  78.2 KB
    Bob

  4. #14
    Join Date
    Jun 2014
    Location
    Denver
    Posts
    31
    Quote Originally Posted by fifty60 View Post
    Thank you for the response. My concern is if the Type Z pressurization can damage the touchscreen. Should the screen have a specific rating for the pressurization?
    I have over 30 installations with HMI touch screens (various mfgr's) and have had zero issues w/ pressure on the panel, nor keeping a purge to meet the purge kit requirements. I think you'll be fine. If you're running anything over a few ounces of pressure/psi, you've got other issues you need to take care of.