Quote Originally Posted by Adamg921 View Post
Rojay, it's a 120/208v 4 wire system. Also, that green wire to "panel ground" would be an EGC and those are bonding jumpers but the only concentric/eccentric knockouts used are on the meter going to the service. I just assumed all service conductor raceways required grounding bushings.
Ok, gotcha. Then you probably didn’t need the grounding bushing and jumper at the top because since the run to your panel is coming from the load side of your service disconnect it’s not really a service raceway but a feeder.