    I'm looking for the uniform code that covers emergency and egress requirements. I'm specifically looking for the code that requires an emergency light over an exterior egress door but on the outside of the door, obviously connected to a backup source.
  2. #2
    Join Date
    Jan 2008
    NC & IN
    Posts
    3,514
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    EC&M had an article on it a while back. The NFPA, UBC and the IBC have had some conflicting verbiage on egress lighting requirements
  3. #3
    Join Date
    Dec 2010
    Posts
    1,459
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The more they overthink the plumbing, the easier it is to stop up the drain
  4. #4
    Join Date
    May 2011
    CA
    Posts
    47
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    as dkidd said, 1006.3 (IBC) is a good place to start.
    From the IBC 2012 Code commentary...
    "Exterior portions of the exit discharge that is immediately adjacent to the building exit discharge door is required to have emergency illumination and not the entire exterior discharge path to the public way."
  5. #5
    Join Date
    Dec 2011
    Ocala, Florida, USA
    Posts
    3,008
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    As far as I understand, the real answer lies with the State you are referring to. Unlike the NEC, which is adopted by all 50 states, Life Safety is usually either NFPA 101 or the IBC. These are then likely modified or even rewritten directly in the State code. So, you have to find out what Life Safety Code your State adopts and refer to it.
    I know what I don't know, and I know where to go to find it!
  6. #6
    Join Date
    May 2011
    CA
    Posts
    47
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Strathead View Post
    This is very true. States may have different guidelines, so check there first. Mine refers back to the IBC. This might help https://codes.iccsafe.org/public/
Posting Permissions
  • You may not post replies
  • You may not edit your posts