    Ground Fault Protection for 480/277 1200 A service?

    I am currently working on a new construction project where we will be interconnecting a solar system with a 480/277 1200 A service. We're planning to do a backfed breaker. According to 230.95 services over 150 V to ground and rated 1000 A or more have to have GFP on the main service and therefore our solar also has to have GFP per 705.32.

    The electrician on the project is telling me they are not installing GFP with the main service breaker because it isn't required for 480/277 services rated 1200 A or less. Am I missing an exception somewhere? I'm hesitant to call the electrician out on this but also want to make sure the customer is getting a code compliant installation. The AHJ enforces 2017 NEC.

  2. #2
    Join Date
    Dec 2011
    Location
    Wisconsin
    Posts
    525
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You are correct.

    230.95 Ground-Fault Protection of Equipment. Ground-fault
    protection of equipment shall be provided for solidly grounded
    wye electric services of more than 150 volts to ground but not
    exceeding 1000 volts phase-to-phase for each service disconnect
    rated 1000 amperes or more. The grounded conductor
    for the solidly grounded wye system shall be connected directly
    to ground through a grounding electrode system, as specified
    in 250.50, without inserting any resistor or impedance device.
    The rating of the service disconnect shall be considered to
    be the rating of the largest fuse that can be installed or the
    highest continuous current trip setting for which the actual
    overcurrent device installed in a circuit breaker is rated or can
    be adjusted.
    Exception: The ground-fault protection provisions of this section shall
    not apply to a service disconnect for a continuous industrial process
    where a nonorderly shutdown will introduce additional or increased
    hazards.

  3. #3
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,918
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by SunFish View Post
    I am currently working on a new construction project where we will be interconnecting a solar system with a 480/277 1200 A service. We're planning to do a backfed breaker. According to 230.95 services over 150 V to ground and rated 1000 A or more have to have GFP on the main service and therefore our solar also has to have GFP per 705.32.

    The electrician on the project is telling me they are not installing GFP with the main service breaker because it isn't required for 480/277 services rated 1200 A or less. Am I missing an exception somewhere? I'm hesitant to call the electrician out on this but also want to make sure the customer is getting a code compliant installation. The AHJ enforces 2017 NEC.
    Note also it's not the service size that triggers the GFP requirement, it's the service disconnect size. You could have a large service with multiple service disconnects under the 2-6 rule and if they were all under 1000a, no GFP required.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  4. #4
    Join Date
    Dec 2006
    Location
    Eastern Oregon
    Posts
    3,653
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Note also it's not the service size that triggers the GFP requirement, it's the service disconnect size. You could have a large service with multiple service disconnects under the 2-6 rule and if they were all under 1000a, no GFP required.
    I agree.

    We've installed many services larger than 1000 amps with multiple service disconnecting means rated less than 1000 amps just so we didn't have to deal with GFP.

  5. #5
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,781
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Cow View Post
    I agree.

    We've installed many services larger than 1000 amps with multiple service disconnecting means rated less than 1000 amps just so we didn't have to deal with GFP.
    Been in that boat also.
    I live for today, I'm just a day behind.

  6. #6
    Join Date
    Oct 2011
    Location
    ID
    Posts
    49
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Ok thanks everybody. The service disconnect is the 1200 A main breaker so it sounds like they should have GFP for this...