    GEC for Manufacturing Machines

    I work in a small industrial plant, and I have to provide electrical utilities for automated assembly machines. Many of these machines have free standing transformers that are fed by the main control panel of the machine. These transformers provide the various voltages that are required by different parts of the machine. In a typical scenario, the machine is installed on site by the manufacturers technicians. I provide the required 480 volt, 3 phase circuit with equipment grounding conductor to the disconnect on the control panel. All other connections (including those of the transformers) are reassembled by the manufacturer's technicians.

    Should I provide a grounding electrode conductor from these transformers to building steel?

  2. #2
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,720
    Look at 250.21 and see if that fits your application.
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.

  3. #3
    Join Date
    Sep 2018
    Location
    Fort Worth, TX USA
    Posts
    2
    Quote Originally Posted by ActionDave View Post
    Look at 250.21 and see if that fits your application.
    Thank you. 250.21 does not cover my application.

  4. #4
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,900
    Quote Originally Posted by Noblink View Post
    Thank you. 250.21 does not cover my application.
    The GEC is required if you have a SDS regardless of whether your system is grounded or not, and 250.21 only tells you when you are allowed to use ungrounded power, which is not relevant to whether you need a GEC or not. There are exceptions for control transformers 1000 VA and less providing power for class 1 and 2 circuits.
    Bob

  5. #5
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    7,933
    You will need to both ground and bond the SDS systems.
    Bonding is via the system bonding jumper
    Grounding, my preference would be building steel. If you need physical protection for the GEC use PVC conduit.