Page 3 of 4 FirstFirst 1234 LastLast
Results 21 to 30 of 31
Thread: Time current curves- why?
  1. #21
    Join Date
    Sep 2004
    Vancouver, WA
    Posts
    711
    History
    If you want to know "why" then you need to consider how relays got their start. Review some of the history. Someone invented this magnetic device that integrates current over time to provide fault protection; do you understand how it works? They made design trade offs. Each designer and manufacturer made different relays, each with different time characteristics, because that was the state of the art. That is how it all started.
    e^(i pi) = -1
  2. #22
    Join Date
    Jan 2008
    Posts
    9,128
    Quote Originally Posted by mbrooke View Post
    General question- why do we have different time current curves? Ie Inverse, Moderately Inverse, Extremely Inverse, ect? I've always imagined that multiples of rated current and time dial settings are enough to acheive selective coordination.
    Current multipliers and time dials, while providing useful curve modification, do not provide the same functionality as the inverse characteristics.
    The inverse characteristics are useful for a few functions that come to mind right off. First, an extremely inverse curve is similar in shape to a distribution fuse and thus coordinates well with both fuses and traditional reclosers.
    Second, a utility distribution system has fault current levels that are mostly a function of line impedance and thus a function of distance from the source. This would less true for impedance-modified systems, short systems, or systems near a relatively large generator. The speed increases as the current increases (as we get closer to the station) and so the inverse curves improve zone coordination with down-line devices.
    They also provide better reaction to cold-load pickup. The sensitivity is less during the short times of temporary overload caused by cold load pickup.
    BB+/BB=?
  3. #23
    Join Date
    Jan 2011
    United States
    Posts
    7,859
    Quote Originally Posted by mivey View Post
    I fully understand- but why not have only one curve- extremely inverse type? What advantage does standard inverse have over extremely inverse is my question I guess. Why can't everything be extremely inverse? When would you use standard inverse?
    I'm in over my head...
  4. #24
    Join Date
    Mar 2003
    Vermont
    Posts
    1,670
    Wouldn't greater inversity {is that a word?} result in less AIC ..???
    ~RJ~
  5. #25
    Join Date
    Jan 2011
    United States
    Posts
    7,859
    Quote Originally Posted by romex jockey View Post
    ~RJ~
    Fault incident energy?
  6. #26
    Join Date
    Mar 2003
    Vermont
    Posts
    1,670
    Quote Originally Posted by beanland View Post
    Someone invented this magnetic device that integrates current over time to provide fault protection; do you understand how it works?.
    I don't know how it works
    I'm asking if there's some relationship between aic (or fie)? and what reacts quicker to it?
    ~RJ~
  7. #27
    Join Date
    Jan 2008
    Posts
    9,128
    Depends on what else you are coordinating with and also the feeder characteristics. Not everything has the same slope in the same overcurrent range.
    BB+/BB=?
  8. #28
    Join Date
    Jan 2008
    Posts
    9,128
    ~RJ~
    There used to be saturation elements to provide relay inversity IIRC but now it is digital math. As for inversity on the line, the fault current decreases with distance of course so we want the inversity to help with zone separation.
    BB+/BB=?
  9. #29
    Join Date
    Mar 2003
    Vermont
    Posts
    1,670
    saturation elements?
    even google is failing me Mivey....
    ~RJ~
  10. #30
    Join Date
    Jan 2008
    Posts
    9,128
    ~RJ~
    I'm not near my references at this time and will have to look later. IIRC, and I may be completely off base, the response would change as the cores approached saturation. Take this for what its worth until I can get back and look through older texts.
    BB+/BB=?
Posting Permissions
  • You may not post replies
  • You may not edit your posts