    Wiring for jockey pump = tap rule?

    If using a pullbox to tap and supply power for a jockey pump controller and a fire pump controller, do these conductors follow the tap rule?

    For instance if a fire pump is a 100 HP, the conductors originating at the pullbox are 500 kcmils but this would make the 3/4 HP jockey pump conductors very over sized if following tap rule?

  2. #2
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    37,928
    Are they service or feeder conductors?

    Tap rules of 240.21 don't apply to service conductors
    I live for today, I'm just a day behind.

  3. #3
    Join Date
    Apr 2012
    Location
    New York
    Posts
    561
    They would be on the load side of the service connect

  4. #4
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    37,928
    Quote Originally Posted by cppoly View Post
    They would be on the load side of the service connect
    Then they are feeder conductors and tap rules apply.

    I haven't done many fire pumps, but from my recollection you need a pretty stout service disconnect rating if it isn't within a listed fire pump controller, as it needs to be able to carry locked rotor current of the fire pump plus any other loads connected indefinitely. Using fire pump controller listed as service equipment and supplying it with service conductors simplifies this issue, someone else designed the overcurrent protection of the assembly.
    I live for today, I'm just a day behind.