    250.68(C)(2)

    250.68(C)(2) states that 'The metal structural frame of a building shall be permitted to be used as a conductor to interconnect electrodes that are part of the grounding electrode system, or as a grounding electrode conductor.' Does this not mean then that the building steel does not have to be a grounding electrode in order to be a conductor between electrodes? For instance, if I had a steel building that was not in direct contact with the earth for 10 ft. or more couldn't I still go from my service disconnect to the building steel and then 100 ft. away go from my building steel to within 5 ft of where my metal water pipe enters the building and be within the code?

  2. #2
    Join Date
    Jan 2008
    Location
    NC & IN
    Posts
    3,421
    Yes , well maybe, but you need grd rods, too.. If I read you correctly. Your building steel does not touch the ground. The water line is the superior grd in this case.

    I was originally thinking you were talking about a separate building.
    Last edited by Buck Parrish; 09-16-18 at 01:53 PM.

  3. #3
    Join Date
    Oct 2014
    Location
    Asheville North Carolina
    Posts
    14
    Thanks for the reply. Yes, the water line would be the main grounding electrode and the steel is not connected to the earth. I could then go from the steel to whatever other electrodes are present, correct?