    Mikesr51
    I’ve got an application where the customer says he’s controlling each of his field lighting pole lights with its own 480 volt 3 phase 80amp breaker. Breakers are beginning to fault. I’m looking for simplest modification to switch with disconnects or lighting contactor/ control box on poles.
    any specific recommendations
  2. #2
    Join Date
    Jun 2003
    Posts
    11,236
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    What do you mean by the breakers are beginning to fault?
    Tom
    TBLO
  3. #3
    Join Date
    Jul 2003
    New Jersey
    Posts
    27,329
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Sounds like the CB's are failing because they're being used as switches. How many 3 pole 80 amp CB's are involved?