    I’ve got an application where the customer says he’s controlling each of his field lighting pole lights with its own 480 volt 3 phase 80amp breaker. Breakers are beginning to fault. I’m looking for simplest modification to switch with disconnects or lighting contactor/ control box on poles.
    any specific recommendations

  2. #2
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,069
    What do you mean by the breakers are beginning to fault?
    Tom
    TBLO

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,030
    Sounds like the CB's are failing because they're being used as switches. How many 3 pole 80 amp CB's are involved?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted