    Lighting controls

    currently we have a building that has 7 contactors controlled by a single control circuit of 277V ( photocell time clock ) contactors have distinct purpose ( one low voltage lighting , one high voltage lighting and emergency exc. My question is , is this acceptable and where can i find related information in the code book?

  2. #2
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,771
    It's a design issue, not a code issue. There is no code reference. I remember working on a K Mart that had the lights on the entire sales floor controlled by one 200A contactor.
    If you don't think too good, don't think too much.

  3. #3
    Join Date
    Sep 2018
    Location
    Dallas, tx
    Posts
    2
    The fact that one 277v emg curcuits contols low voltage high voltage normal and emergency is not an issue ? That was my concern

  4. #4
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,771
    Quote Originally Posted by Michael B2356 View Post
    The fact that one 277v emg curcuits contols low voltage high voltage normal and emergency is not an issue ? That was my concern
    I'm not quite sure what you mean. Look at 700.12(F).
    If you don't think too good, don't think too much.