    AC PVC disconnect tap from supply side

    I have service conductor on the line side of service disconnect tapped to an AC PV main disconnect. The question is should the neutral and ground bar of the Alternating Current (AC) PV main disconnect be bonded together i.e. main bonding jumper be in the AC PV main disconnect per NEC 2014 690 or possibly 705?????

  2. #2
    Join Date
    May 2011
    Posts
    4,763
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Good question. There have been some knock down drag out arguments over this one in the past on this forum.

    My advice. Decide if you want it to be a 'service disconnect', for any reason. If you do, bring the neutral there and put an MBJ. If you don't then run an EGC from the other service disconnect and leave neutral floating. Whichever you want, run it by your AHJ before installing. If it's a small system and/or you don't really have time for that, plan in such a way that you could do whichever the AHJ asks.

    For what it's worth, in the 2020 NEC draft, the CMP seems to be moving away from the opinion that it's a service disconnect, without quite making that explicit. On the other hand, the definition of a service looks to be changing and that will take away one of the biggest arguments that it is not a service disconnect.

  3. #3
    Join Date
    Nov 2015
    Location
    CA, USA
    Posts
    705
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Go with what the AHJ wants. The NEC does not require one or the other, some AHJs will allow either and some only allow one. I expect there to be clarity in the 2020 NEC on the subject based on the drafts I have seen.

  4. #4
    Join Date
    May 2013
    Location
    Massachusetts
    Posts
    2,423
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    This could come up in two different situations, where the AHJ / interpretation of the NEC might have a different answer in each.

    1. A hot sequence meter for the building loads exists. You intend to connect between this hot sequence meter, and the corresponding main disconnect. Your PV system is still on the same service ("behind the meter"), but has a separate service disconnect. The main reason you might do this, is that system size makes it impractical to use the 120% rule and do a load side interconnection.

    2. Your PV system will be a separate service from the service that feeds the building loads, but it will ultimately use the same utility-owned transformer and the same service conductors that drop from the transformer secondary. It connects on the line side of both the main service disconnect, and the meter for the main service that feeds building loads. It therefore has its own service disconnect, and its own utility service meter.

  5. #5
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    10,270
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by pv_n00b View Post
    Go with what the AHJ wants. The NEC does not require one or the other, some AHJs will allow either and some only allow one. I expect there to be clarity in the 2020 NEC on the subject based on the drafts I have seen.
    You are correct, sir. I went to a lecture at SPI on the 2017 and 2020 NEC given by a member of the group who are writing the code for 690 and related sections. She said that in 2020 the NEC will require N-G bonding at the disco for supply side PV interconnections.

  6. #6
    Join Date
    Jun 2018
    Location
    Glen bunie, md, us
    Posts
    131
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    Good question. There have been some knock down drag out arguments over this one in the past on this forum.

    My advice. Decide if you want it to be a 'service disconnect', for any reason. If you do, bring the neutral there and put an MBJ. If you don't then run an EGC from the other service disconnect and leave neutral floating. Whichever you want, run it by your AHJ before installing. If it's a small system and/or you don't really have time for that, plan in such a way that you could do whichever the AHJ asks.

    For what it's worth, in the 2020 NEC draft, the CMP seems to be moving away from the opinion that it's a service disconnect, without quite making that explicit. On the other hand, the definition of a service looks to be changing and that will take away one of the biggest arguments that it is not a service disconnect.
    The power flows from solar panels system to the AC PV main disco which outputs power to utility grid if the AC main disco is tapped from supply side of service disco feeding bldg. In normal secanrio without solar panel you have power flow from utility to service disco to the bldg.

    How can one decide if AC PV disconnect is to be used as service disco?

    Sent from my SM-G935U using Tapatalk

  7. #7
    Join Date
    May 2011
    Posts
    4,763
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hhsting View Post
    The power flows from solar panels system to the AC PV main disco which outputs power to utility grid if the AC main disco is tapped from supply side of service disco feeding bldg. In normal secanrio without solar panel you have power flow from utility to service disco to the bldg.

    How can one decide if AC PV disconnect is to be used as service disco?
    What I was trying to say was that there might be some reason, relating to the site details, that you prefer or don't prefer to bring a separate EGC to the solar disco. Whatever you prefer, run it by the AHJ before building.

    The other advice given - ask the AHJ from the get go how they would like it done - is also good advice. Let them decide for you, especially if it makes no major difference to your bottom line.

  8. #8
    Join Date
    Jun 2018
    Location
    Glen bunie, md, us
    Posts
    131
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    What I was trying to say was that there might be some reason, relating to the site details, that you prefer or don't prefer to bring a separate EGC to the solar disco. Whatever you prefer, run it by the AHJ before building.

    The other advice given - ask the AHJ from the get go how they would like it done - is also good advice. Let them decide for you, especially if it makes no major difference to your bottom line.
    AHJ says follow NEC 2014 . So if I do not place Main Bonding Jumper in the main PV AC disco and bring 3 phase conductors, 1 neutral to neutral bar from service conductor tap into PV AC main disconnect and bring 1 EGC from bldg main service disconnect ground bar into PV AC main disco ground bar that would also be ok?

  9. #9
    Join Date
    May 2011
    Posts
    4,763
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hhsting View Post
    AHJ says follow NEC 2014 . So if I do not place MBJ in the main PV AC disco and bring 3 phase, 1 neutral from service conductor tap and bring 1 EGC from bldg main service disconnect ground bar into PV AC main disco that would also be ok?
    ...
    AHJ evidently has not considered the question before, or doesn't want to consider it, since 'follow the code' is a bit too vague on this point.

    What you propose would be okay with some. Have you drawn it up and submitted plans?

    I do believe that the disco must meet KAIC requirements and that it be suitable for use as service equipment even if you don't call it that. The utility might ask after that even if the AHJ doesn't.

  10. #10
    Join Date
    Jun 2018
    Location
    Glen bunie, md, us
    Posts
    131
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Current always goes back to the source so been told in fudamental electrical classes
    So if there is a fault in PV solar system will it go to the place there is fault then to EGC to wherever MBJ is and then to what electric utility or back to solar panels? Its confusing and very confusing to place MBJ or not AC PV disconnect.