    Table 220.88

    (I search the previous entry and this topic was closed. I have a question and opening a new one).

    I took 4 different kVA value and implemented the Optional method for Table 220.88.
    Attached is the results.

    Why Not All Electric Restaurant always have more kVA rating (therefore bigger service conductor size and OCPD) than All Electric Restaurant?
    What I Click image for larger version. 

Name:	Table 220.88.jpg 
Views:	44 
Size:	106.3 KB 
ID:	21279am missing here?
    Attached Images Attached Images  

  2. #2
    Join Date
    Mar 2017
    Location
    Newark, NJ
    Posts
    64
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    no one has any idea?
    Was I the only one who is thinking south?

  3. #3
    Join Date
    Mar 2017
    Location
    Newark, NJ
    Posts
    64
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    helloooo.

  4. #4
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,011
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    It's Saturday not a lot of members on here and probably many don't want to do a calculation. I am getting ready to go out but I will look at it latter
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  5. #5
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,011
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    I took a quick look and I have no idea why all electric gets the demand factor especially in a restaurant.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  6. #6
    Join Date
    Mar 2017
    Location
    Newark, NJ
    Posts
    64
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dennis Alwon View Post
    I took a quick look and I have no idea why all electric gets the demand factor especially in a restaurant.
    That is what I am saying!!! All electric restaurant will have a smaller service cable than not all electric restaurant. What I am missing???